Grounding and Isolation transformer settings

Created: Aug 23, 2021 06:18:00Latest reply: Aug 23, 2021 10:19:51 436 20 1 0 0
  Rewarded HiCoins: 1 (problem resolved)

In HUAWEI there is a setting name Isolation transformer settings. One setting is Input not grounded without a transformer and the other is Input not grounded with a transformer. What are these settings meant for and how it is applicable with different scanarios??

Featured Answers

Best answer

Recommended answer

gzzz
Admin Created Aug 23, 2021 06:53:05

Hello friend
The isolation setting is to set the inverter to work according to the grounding status of the DC side and the connection status to the grid.
When the PV-is grounded, the isolation transformer must be connected, set to "input grounded, with transformer"; when the PV-is not grounded, set to "input not grounded, with/without transformer".

View more
  • x
  • convention:

Hamid_Raza_Naveed
Hamid_Raza_Naveed Created Aug 23, 2021 10:15:37 (0) (0)
Hello, but there isn't any option for "input grounded, with transformer"  
gzzz
gzzz Reply Hamid_Raza_Naveed  Created Aug 24, 2021 01:35:56 (0) (0)
Hello, friend.
This problem is caused by different access modes.
Input grounding with a transformer: Used when PV modules are grounded. In this scenario, an isolation transformer must be installed. In this case, the N-to-PE voltage must be greater than 30 V.  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Created Sep 11, 2021 06:35:28 (0) (0)
One of our installer set it to " Input not grounded, with a transformer" because his PV is grounded but after few minutes a fault occurs: Alarm No: 2064 and Cause ID:2
and inverter shut down
what could be the issue here??
please guide  
gzzz
gzzz Reply Hamid_Raza_Naveed  Created Sep 11, 2021 07:24:41 (0) (0)
Hello, friend.
I think the problem is a setup error.
For PV-grounding, an isolation transformer must be connected and set to "Input grounding with transformer"
I hope this helps you.
Thank you.  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Reply gzzz  Created Sep 11, 2021 07:31:56 (0) (0)
Actually due to abnormal grounding alarm, inverter wasn't producing but as soon as he set the setting to " Input not grounded, with a transformer", inverter start producing and in 25 minutes it shuts down giving the alarm of device fault i mentioned in previous comment with you  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Reply gzzz  Created Sep 11, 2021 07:33:00 (0) (0)
and when that alarm occured he quickly changed setting to " Input not grounded, without a transformer" and then he again had abnormal grounding alarm.  
gzzz
gzzz Reply Hamid_Raza_Naveed  Created Sep 11, 2021 08:19:09 (0) (0)
Hello, friend.
In your case, we recommend that you contact the PV Center with the SN number of the inverter and describe the problem you are experiencing. You can send an email to the following email box and they will provide you with support.
Europe Email: eu_inverter_support@huawei.com
China and Asia Pacific: solarservice@huawei.com
Latin America: Email: la_inverter_support@huawei.com
I hope this helps you.
Thank you.  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Reply gzzz  Created Sep 11, 2021 09:25:52 (0) (0)
One last thing Voltage between neutral and ground is 50V
Can I apply Input ground with a transformer?  
gzzz
gzzz Reply Hamid_Raza_Naveed  Created Sep 11, 2021 09:46:56 (0) (0)
Hello, friend.
I don't know what you mean. Can you make it clear?  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Reply gzzz  Created Sep 11, 2021 11:21:51 (0) (0)
what i mean is that installer checked that voltage between nuetral terminal and ground terminal (N-PE) is 50V
so can he change Isolation configuration to Input ground with a transformer????  
All Answers
Hello, dear.
It's nice to meet you in the community.
We're working on getting the right answer for you. Please rest assured that we'll be back with an answer shortly.
View more
  • x
  • convention:

gzzz
gzzz Admin Created Aug 23, 2021 06:53:05

Hello friend
The isolation setting is to set the inverter to work according to the grounding status of the DC side and the connection status to the grid.
When the PV-is grounded, the isolation transformer must be connected, set to "input grounded, with transformer"; when the PV-is not grounded, set to "input not grounded, with/without transformer".

View more
  • x
  • convention:

Hamid_Raza_Naveed
Hamid_Raza_Naveed Created Aug 23, 2021 10:15:37 (0) (0)
Hello, but there isn't any option for "input grounded, with transformer"  
gzzz
gzzz Reply Hamid_Raza_Naveed  Created Aug 24, 2021 01:35:56 (0) (0)
Hello, friend.
This problem is caused by different access modes.
Input grounding with a transformer: Used when PV modules are grounded. In this scenario, an isolation transformer must be installed. In this case, the N-to-PE voltage must be greater than 30 V.  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Created Sep 11, 2021 06:35:28 (0) (0)
One of our installer set it to " Input not grounded, with a transformer" because his PV is grounded but after few minutes a fault occurs: Alarm No: 2064 and Cause ID:2
and inverter shut down
what could be the issue here??
please guide  
gzzz
gzzz Reply Hamid_Raza_Naveed  Created Sep 11, 2021 07:24:41 (0) (0)
Hello, friend.
I think the problem is a setup error.
For PV-grounding, an isolation transformer must be connected and set to "Input grounding with transformer"
I hope this helps you.
Thank you.  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Reply gzzz  Created Sep 11, 2021 07:31:56 (0) (0)
Actually due to abnormal grounding alarm, inverter wasn't producing but as soon as he set the setting to " Input not grounded, with a transformer", inverter start producing and in 25 minutes it shuts down giving the alarm of device fault i mentioned in previous comment with you  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Reply gzzz  Created Sep 11, 2021 07:33:00 (0) (0)
and when that alarm occured he quickly changed setting to " Input not grounded, without a transformer" and then he again had abnormal grounding alarm.  
gzzz
gzzz Reply Hamid_Raza_Naveed  Created Sep 11, 2021 08:19:09 (0) (0)
Hello, friend.
In your case, we recommend that you contact the PV Center with the SN number of the inverter and describe the problem you are experiencing. You can send an email to the following email box and they will provide you with support.
Europe Email: eu_inverter_support@huawei.com
China and Asia Pacific: solarservice@huawei.com
Latin America: Email: la_inverter_support@huawei.com
I hope this helps you.
Thank you.  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Reply gzzz  Created Sep 11, 2021 09:25:52 (0) (0)
One last thing Voltage between neutral and ground is 50V
Can I apply Input ground with a transformer?  
gzzz
gzzz Reply Hamid_Raza_Naveed  Created Sep 11, 2021 09:46:56 (0) (0)
Hello, friend.
I don't know what you mean. Can you make it clear?  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Reply gzzz  Created Sep 11, 2021 11:21:51 (0) (0)
what i mean is that installer checked that voltage between nuetral terminal and ground terminal (N-PE) is 50V
so can he change Isolation configuration to Input ground with a transformer????  

Png

Please see this image there is no option of input grounded with transformer. The only options are two which can be seen. We can select any option when PV is not grounded??

View more
  • x
  • convention:

BetterMing
BetterMing Created Aug 23, 2021 10:55:08 (0) (0)
Yes two options, choose according to the actual one.  
gzzz
gzzz Created Aug 24, 2021 01:37:47 (0) (0)
Hello, friend.
This problem is caused by different access modes.
Input grounding with a transformer: Used when PV modules are grounded. In this scenario, an isolation transformer must be installed. In this case, the N-to-PE voltage must be greater than 30 V.
When PV is not grounded, choose according to the actual situation  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Reply BetterMing  Created Aug 24, 2021 05:13:54 (0) (0)
can you please elaborate what each options are used for and how they are different from each other  
Ming_Li
Ming_Li Reply Hamid_Raza_Naveed  Created Aug 27, 2021 08:06:36 (0) (0)
This is to prevent a safety accident, PV- grounding may cause the inverter to burn out.  
Hamid_Raza_Naveed
Hamid_Raza_Naveed Reply Ming_Li  Created Sep 11, 2021 12:25:04 (0) (0)
Thankyou for your response, let me clarify the scenario here for you.
Inverter is 60KTL M0 and inverter is grounded. Now the issue installer is facing that its continuously showing abnormal grounding error and when he checked N-PE voltage it was 50V.
Should i ask him to work on his earthing pits performance or changing Isolation configuration to Input not ground with a transformer will solve the issue?  

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.