[Function configuration] The UPS2000-G-15 kVA/20 kVA is parallel and the battery packs are shared. How to set the battery parameters

Latest reply: Apr 20, 2022 16:05:41 85 2 1 0 1

Hello friends of the forum, today I share about the UPS2000 shared lead-acid batteries.


【Principles and calculation methods】


  1. If a UPS2000-G-15 kVA/20 kVA parallel system shares a battery string, set the same battery string capacity and charge current for each UPS.


2.Battery capacity (Ah) = ( Capacity of a single battery string )x (Number of parallel battery strings)/(Number of parallel UPSs sharing a battery string). 


Maximum charge current (Ah) = 0.1 x Capacity of a single battery string x Number of parallel battery strings/Number of parallel UPSs sharing a battery string.If the calculated maximum charge current is greater than 4 A, set it 4 A. 


3.If a single 15 kVA/20 kVAUPS connects to two battery packs, the maximum charge current must be less than or equal to 2.0 A



【Example 1】


Two UPSs sharing a 65 Ah battery string as an example: 

Capacity of a single battery string=65Ah;

Number of parallel battery strings=1;

Number of parallel UPSs sharing a battery string=2;

the calculated battery capacity is 65 x 1/2 Ah= 32.5 Ah, You can set the battery capacity of each UPS to 32 Ah; 

the calculated maximum current is 0.1 x 65 x 1/2 A= 3.25 A, You can set the battery charging current for each UPS  to 3.0 A.



【Example 2】


If the 15 kVA/20 kVA UPS parallel system shares battery packs, refer to the cable connection methods shown in the following figure. 


11


The connection shown below is explained as follows:battery packs 1 and 2 are in series, battery packs 3 and 4 are in series, battery packs 5 and 6 are in series, and battery packs 7 and 8  are in series. battery packs 1, 3, 5, and 7 are in parallel and battery packs 2, 4, 6, and 8  are in parallel.


Please note:When battery packs are connected in series or parallel, only battery packs of the same model and specifications can be installed or replaced. Do not use battery packs of different models or specifications together.


Other parameters: the capacity of each battery pack is 65Ah.


Capacity of a single battery string=65Ah;

Number of parallel battery strings=4;

Number of parallel UPSs sharing a battery string=2;


the calculated battery capacity is 65 x 4/2 Ah= 130 Ah, You can set the battery capacity of each UPS to 130 Ah; 

the calculated maximum current is 0.1 x 65 x 4/2 A= 13 A>4A, You can set the battery charging current for each UPS  to 4.0 A.


That's all I have to share today, thank you for reading!








A.

The post is synchronized to: uninterruptible power supply 2000/5000

Thanks for sharing.
View more
  • x
  • convention:

Well done. Thank you
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.