In some scenarios, the customers want to change the value of active power produced by the inverter.
This can be done throw various ways, one of them is by changing one parameter from inverter settings/fusion solar.
In order to use this, the inverter needs to be connected to Fusion solar and need to be online.
Scenario:
Customer X had set on active power 50KW but now he wants to put 66KW. He tried to modify the value from Fusion Solar but it doesn't work, the maximum value that he can set is 50KW.
At this moment customer X thinks the inverter is damaged or doesn't work as it should be, but the issue is somewhere else, one parameter doesn't allow to set a higher value on active power.
In the next pictures will see what is that parameter.


The parameter that set the maximum value on active power is Active power baseline, if this parameter is set to 50 KW the maximum value that can be set on Active power derating will be 50 KW, so to use the entire power of the inverter need to set on Active power baseline maximum value of 66KW.
After this is set also the first parameter can be set as well.