Faults and Alarms of Inverters in the Same Combiner Box

Latest reply: Mar 12, 2021 12:42:41 183 1 2 0 0


1. The SUN2000 does not generate power and cannot be connected to the grid. The SUN2000 generates an alarm indicating that the grid voltage is abnormal (301-4). The voltage of one phase is only 101 V. Ask the customer to check the actual voltage.

140209hcv74ceiyvo107se.png

After onsite check, it is found that multiple inverters that report alarms are under the same combiner box. Check the input and output voltages of the combiner box. A copper bar at the main switch of the combiner box is burnt. It is suspected that the internal screws are not tightened, if the switch is damaged due to long-time running, replace the switch and copper bar.

2. Multiple inverters are faulty and cannot run.

According to the log analysis, the SUN2000 runs properly on the day and shuts down properly at night. The SUN2000 fails to run after it is started on the next day, and no abnormal alarm information is reported. The logs of several SUN2000s show the same symptom,

Check the logs carefully. The SUN2000 shuts down for a period of time at night and triggers another data record, as shown in the following figure.

 原图2

原图1

 

At this time, the DC auxiliary power supply of the inverter starts again. There is no DC voltage at night. Therefore, the auxiliary power supply starts due to lightning strikes. In addition, the current day is also a thunderstorm. Therefore, the problem is caused by lightning strikes.

Check for lightning strikes:

1. Some inductive lightning strikes may be far away from the site, and the lightning strike points may not be located on the onsite device.

2. Components are damaged, PV modules are broken, or the junction box is bulged. This may be caused by local lightning strikes.

Check whether there are blackouts caused by lightning strikes around the inverter.

How to prevent:

1. Ensure that the ground points of each PV module and support are properly connected to the ground bar and are properly grounded. Check the ground points periodically.

2. The shells of the SUN2000 in the combiner box are grounded properly and are properly grounded to the ground grid.

3. Lightning protection devices are properly installed. Some small power plants are equipped with large surge protection modules. Inductive lightning may cause device damage. However, the surge protection modules may not work. Therefore, you can design a good surge protection capability based on the actual situation.

 

Good prevents
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.