NE05E-SE/NE05E-SF Environmental Requirements
Specific Environmental Requirements
Storage requirements http://support.huawei.com/huaweiconnect/public_sys-resources/icon-note.gif NOTE: The storage environment must comply with ETSI EN 300 019-1-1.
5 Hz to 10 Hz
10 Hz to 50 Hz
50 Hz to 100 Hz
The air is free from explosive, electric-conductive, magnetic-conductive, or corrosive dust.
The concentrations of mechanically active substances meet the requirements defined in the following table.
Suspended dust ≤ 5.00 mg/m3 Deposited dust ≤ 20.0 mg/(m2·h) Gravel ≤ 300 mg/m3 The concentrations of chemically active substances meet the requirements defined in the following table.
SO2 ≤ 0.30 mg/m3 H2S ≤ 0.10 mg/m3 NO2 ≤ 0.50 mg/m3 HF ≤ 0.01 mg/m3 NH3 ≤ 1.00 mg/m3 Cl2 ≤ 0.10 mg/m3 HCl ≤ 0.10 mg/m3 O3 ≤ 0.05 mg/m3 Ensure that the location where the equipment is stored is free from microbial infestation.
There are no rodents, such as mice.
The packaging is intact.
Rainproof measures are taken to prevent water from entering the packaging.
No water accumulates under the packaging.
The packaging is not exposed to sunlight.
Climate requirements
Temperature -40ºC to +70ºC (-40ºF to +158ºF) Relative humidity 5% to 100% Temperature change rate ≤ 1ºC/min Atmospheric pressure 70 kPa to 106 kPa Solar radiation ≤ 1120 W/m2 Heat radiation ≤ 600 W/m2 Waterproof requirements
For equipment at a customer site, it is recommended that the equipment be stored indoors.
Ensure that no water accumulates on the floor or drops to the equipment packaging. Keep the equipment away from places where water is apt to leak, such as the places near automatic fire-fighting facilities and heating facilities.
If the equipment has to be stored outdoors, ensure that:Biological environment requirements
Air cleanness requirements
Mechanical stress requirements
Random vibration Acceleration 0.02 m2/s3 Frequency dB/oct -12 to +12
Transportation environment requirements http://support.huawei.com/huaweiconnect/public_sys-resources/icon-note.gif NOTE: The transportation environment must comply with ETSI EN 300 019-1-2.
5 Hz to 20 Hz
20 Hz to 200 Hz
The air is free from explosive, electric-conductive, magnetic-conductive, or corrosive dust.
The concentrations of mechanically active substances meet the requirements defined in the following table.
Deposited dust ≤ 3.0 mg/(m2·h) Gravel ≤ 100 mg/m3 The concentrations of chemically active substances meet the requirements defined in the following table.
SO2 ≤ 1.00 mg/m3 H2S ≤ 0.50 mg/m3 NO2 ≤ 1.00 mg/m3 HF ≤ 0.03 mg/m3 NH3 ≤ 3.00 mg/m3 HCl ≤ 0.50 mg/m3 O3 ≤ 0.10 mg/m3 Ensure that the location where the equipment is placed is free from microbial infestation.
There are no rodents, such as mice.
The equipment packaging is intact.
Rainproof measures are taken for the transportation tools to prevent water from entering the packaging.
No water accumulates in the transportation tools.
Climate requirements
Temperature -40ºC to +70ºC (-40ºF to +158ºF) Relative humidity 5% to 95% Temperature change rate ≤ 1ºC/min Atmospheric pressure 70 kPa to 106 kPa Solar radiation ≤ 1120 W/m2 Heat radiation ≤ 600 W/m2 Waterproof requirements
Biological environment requirements
Air cleanness requirements
Mechanical stress requirements
Random vibration Acceleration 1 m2/s3 Frequency dB/oct -3 Collision Shock response spectrum I (sample weight > 50 kg) 100 m/s2, 11 ms, 100 times on each side Shock response spectrum II (sample weight ≤ 50 kg) 180 m/s2, 6 ms, 100 times on each side NOTE: Shock response spectrum is a curve of the maximum acceleration responses generated by the equipment under specified impact excitation.
Operating environment requirements
http://support.huawei.com/huaweiconnect/public_sys-resources/icon-note.gif NOTE: The operating environment must comply with ETSI EN 300 019-1-3.5 Hz to 62 Hz
62 Hz to 200 Hz
The air is free from explosive, electric-conductive, magnetic-conductive, or corrosive dust.
The concentrations of mechanically active substances meet the requirements defined in the following table.
Suspended dust ≤ 0.4 mg/m3 Deposited dust ≤ 15 mg/(m2·h) Gravel ≤ 300 mg/m3 The concentrations of chemically active substances meet the requirements defined in the following table.
SO2 ≤ 0.30 mg/m3 H2S ≤ 0.10 mg/m3 NO2 ≤ 0.50 mg/m3 HF ≤ 0.01 mg/m3 NH3 ≤ 1.00 mg/m3 Cl2 ≤ 0.10 mg/m3 HCl ≤ 0.10 mg/m3 O3 ≤ 0.05 mg/m3 Ensure that the location where the equipment is installed is free from microbial infestation.
There are no rodents, such as mice.
When the equipment is installed in a network cabinet, the temperature at the air intake vent of the network cabinet must be within the range of -40°C to 55°C (-40°F to 131°F). For details on the requirements for network cabinets, see the Installation Guide.
When the equipment is installed in an APM30 outdoor cabinet, the temperature at the air intake vent of the outdoor cabinet must be within the range of -40°C to 55°C (-40°F to 131°F). For details on the requirements for outdoor cabinets, see the Installation Guide.
If the equipment is installed in a cabinet, the impact of radiation can be ignored. If the equipment is installed outdoors, proper protection must be provided for the equipment against radiation.
The temperature and relative humidity are measured at the place 1.5 m (4.92 ft) above the floor and 0.4 m (1.31 ft) away from the front side of a cabinet without any front or rear protection panel.
Temperature range: 15ºC to 30ºC (59ºF to 86ºF)
Relative humidity range: 40% to 75%
Climate requirements
-40ºC to +65ºC (-40ºF to +149ºF) 5% to 95% NOTE:
To improve product application reliability, it is recommended that a dedicated precision air conditioner be installed in an equipment room and the temperature and relative humidity be controlled within the following ranges:
http://support.huawei.com/huaweiconnect/public_sys-resources/icon-note.gif NOTE: Do not install the air conditioner above the equipment and ensure that the air exhaust vent of the air conditioner does not face the equipment. Keep the air conditioner away from a window as far as possible to ensure that no moisture from the window is blown towards the equipment through the air conditioner.Altitude ≤ 4000 m (13123.2 ft)
(When the altitude is lower than 1800 m (5905.44 ft), the equipment operates normally. When the altitude is within the range from 1800 m to 4000 m (from 3280.8 ft to 13123.2 ft), the actual equipment operating temperature decreases by 1ºC (1.8ºF) for every 220 m (721.78 ft) increase in altitude.)Temperature change rate ≤ 0.5ºC/min Wind speed ≤ 5 m/s Solar radiation ≤ 700 W/m2 Heat radiation ≤ 600 W/m2 Biological environment requirements
Air cleanness requirements
Mechanical stress requirements
Sinusoidal vibration Velocity ≤ 5 mm/s Acceleration ≤ 2 m/s2 Frequency Collision Shock response spectrum II Half-sine wave, 30 m/s2, 11 ms, 3 times on each side Static payload 0 kPa NOTE: Shock response spectrum is a curve of the maximum acceleration responses generated by the equipment under specified impact excitation. Static payload refers to the capability of the equipment in package to bear the pressure from the top in normal pile-up method.
Environmental Standards and Protocols Compliant
| ETSI EN 300 019-1-1 | Environmental Engineering (EE) Environmental conditions and environmental tests for telecommunications equipment Part 1-1: Classification of environmental conditions; Storage Class 1.1: Weatherprotected, partly temperature-controlled storage locations Class 1.2: Weatherprotected, not temperature-controlled storage locations |
| ETSI EN 300 019-1-2 | Environmental Engineering (EE) Environmental conditions and environmental tests for telecommunications equipment Part 1-2: Classification of environmental conditions; Transportation Class 2.1: Very careful transportation Class 2.2: Careful transportation |
| ETSI EN 300 019-1-3 | Environmental Engineering (EE) Environmental conditions and environmental tests for telecommunications equipment Part 1-3: Classification of environmental conditions Class 3.1: Temperature-controlled locations Class 3.2 Partly temperature-controlled location |
| IEC 60068-2 | Basic Environmental Testing Procedures |
| IEC 60721-2-6 | Environmental conditions appearing in nature - Earthquake vibration |
| IEC 60721-3-1 | Classification of environmental conditions Part 3: Classification of groups of environmental parameters and their severities Section 1: Storage |
| IEC 60721-3-3 | Classification of environmental conditions Part 3: Classification of groups of environmental parameters and their severities Section 3: Stationary use at weatherprotected locations |
| ETSI EN 300 753 | Equipment Engineering (EE) Acoustic noise emitted by telecommunications equipment |
| ROHS | Restriction of the use of certain hazardous substance in electrical and electronic equipment |
If you have any problems, please post them in our Community. We are happy to solve them for you!