Downgrade the OLT to an earlier version. After the OLT is successfully added to the U2000, the OLT data fails to be synchronized to the U2000. As a result, the OLT cannot be managed on the U2000.

             Handling Procedure

  Step 1    Check SNMP configurations.

snmp-agent target-host trap-hostname U2000_237 address 100.104.145.237 trap-paramsname public123

snmp-agent target-host trap-paramsname public123 v1 securityname public123

snmp-agent trap enable standard

snmp-agent trap source meth 0

snmp-agent community read public123

snmp-agent community write private123

Check the firewall enabling statue.

HT(config)#display sysman firewall
{ protocol-type<E><telnet,ssh,snmp> }:snmp

Command: 
display sysman firewall snmp
Firewall is disabled

HT(config)#

If the firewall is enabled, add the NMS address to the whitelist.

MA5680T(config)# sysman firewall snmp enable
MA5680T(config)# display sysman firewall snmp
Firewall is enabled

    Step 2    Configure an IP address allowed by the SNMP.

MA5680T(config)# sysman ip-access snmp 100.104.145.237 100.104.145.237
MA5680T(config)#display sysman ip-access snmp
IP-Access Table:
--------------------------------------------
Index Start-IPAddr End-IPAddr
--------------------------------------------
1 100.104.145.237 100.104.145.237
--------------------------------------------

Note: If all configurations are normal but data synchronization still fails, check OLT configurations such as the IP address and all routes. If the routes are normal, the U2000 server can be successfully pinged.

To add a static route if required for the check, run the IP route-static command.

 Step 3    Suspect that the data synchronization fails because the TCP connection fails to be set up. As a result, the OLT cannot be pinged from the U2000 server, or OLT configurations cannot be backed up to the U2000 server.

In an attempt to back up the configurations, the system displays a message indicating that the server is unreachable.

 Step 4    Capture packets on the U2000 server.

171053weej4movr91rvozj.png?111.jpg.png


set up after a TCP connection is successfully set up.

 Step 5    Configure the OLT for management through the upstream port. The configuration method is as follows:

1.       Set the upstream Native VLAN to 200 (or to another VLAN ID).

HT(config)#port vlan 300 0/19 0                                                                                                     
                                                                                                                                    
HT(config)#interface giu 0/19

HT(config-if-giu-0/19)#native-vlan
{ all<K>|portid<U><0,1> }:0 vlan 300

Command: 
native-vlan 0 vlan 300

2.       On the interface for VLAN 300 configuration, configure the management IP address of the OLT.

56(config)#interface vlanif 300

56(config-if-vlanif300)#

56(config-if-vlanif300)#

56(config-if-vlanif300)#ip address 1.1.1.1 23
{ <cr>|description<K>|sub<K> }:

Command: 
ip address 1.1.1.1 23

56(config-if-vlanif300)#

  Step 6   Capture packets by mirroring on the upstream port of the OLT.

Note: Mirror the packets of port 0/19/0 to a port on another upstream interface and ensure that the 2 ports are in the same VLAN so that the packets can be transmitted in between.

56(config)#mirror port src-port 0/19/0 dst-port 0/20/0
{ mirror-direction<E><ingress,egress,all> }:all

Command: 
mirror port src-port 0/19/0 dst-port 0/20/0 all
! RUNNING MAJOR 2018-11-21 11:49+08:00
EVENT NAME :Configure the port mirror
PARAMETERS :Source frame ID: 0, Source slot ID: 19, Source port ID: 0,
Destination frame ID: 0, Destination slot ID: 20, Destination port ID: 0,
Mirror direction: all

56(config)#

  Step 7    Query packet capture data.


171230rzzk0i88x0xi70p7.png?112.jpg.png

According to the captured packets, the OLT does not reply to the last ACK packet. As a result, the three-way handshake fails.

 Step 8   Analyze the cause why the OLT does not reply to the packet.

According to an analysis, it is found that the OLT considers that the received packet checksum is incorrect.

Root cause: The advanced option Checksum Offload of the network adapter of the U2000 server is enabled, causing a problem with the compatibility with the OLT. After the option is disabled, services are restored.

171319i3b5ugkfledtiid3.png?113.png

good
View more
  • x
  • convention:

Great
View more
  • x
  • convention:

Nice
View more
  • x
  • convention:

note
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.