ETP48200 Power system DC output testing

Latest reply: Feb 7, 2022 06:24:12 2069 17 23 0 2

Scenario:

Power system is installed with battery support and has no load connection. It's a capacity testing whether it can deliver at particualr value of low voltage or high voltage DC output based on customer's load requirement.


Objective:

Must measure the DC output and it should within the range of 43.2 to 57.6 Vdc. More clearly, need to get low voltage reading at 42Vdc and high voltage at 58Vdc.


Concept:

Bus bar voltage: 53.5V, if the battery connects to the power system,the busbar voltage is the batttery voltage. In other words, if we connect the battery, the voltage what we test is the battery voltage.


Procedure:

Note : Turn Off the battery if you need to measure the DC voltage at low level and high level depending on requirement.

151756m0ohbqohpdsnt5ln.jpg?LCD menu TP48

151810ga4e8fex9e7xoaxf.jpg?LCD menu TP48


Step 1 :

Main Menu/ Parameters settings (default password :000001#) / Power System /AC&DC Volt. Para. / Bus Ultra UV Thres. : 44 V→ 40V, Bus Bar UV Thres. :45V→ 40V.


Step 2:

Main Menu/ Running Control (default password :000001#)/Power System/System Control Mode/Automatic→Manual, Rectifier / Rectifier Group / Manual Control Volt./53.5V→42V


Step 3:

Measure the DC output, it should decresed to 42Vdc at screen. Repeat the step 1 & 2 for high voltage, set in overvoltage parameter. Then, measure the DC output, it should get nearly 58Vdc. 


Step 4 :

After doing measurement, restore back the default setting or set the system control mode to Automatic.




good case.
View more
  • x
  • convention:

Possible to have output of 48V while the battery is connected to? Or it will still be battery depended voltage once the battery is connected?
View more
  • x
  • convention:

Good sharing, Sassi.
View more
  • x
  • convention:

Systematic explaination
View more
  • x
  • convention:

very clear documentation. Great sharing.
View more
  • x
  • convention:

Good share
View more
  • x
  • convention:

Good case
View more
  • x
  • convention:

how many rectifier needed at least for a ETP to supply power with and without load connection?
View more
  • x
  • convention:

Sassi
Sassi Created Jun 19, 2019 10:18:54 (0) (0)
if no battery and no load connected, 1 rectifier module can power on the system. because the battery charge current limit is 0.1C or 0.15C,so the battery charge current is 15A or 22.5A , i think the rated current of the rectifier module is 50A. By having 30% load, you can have at least 2 rectifier.  
Posted by Yoge at 2019-06-19 09:45 Possible to have output of 48V while the battery is connected to? Or it will still be battery depend ...
of course we still can get 48V by having connected to battery, just power off AC input ,and use battery discharge ,and you can get 48V for several minutes later.
View more
  • x
  • convention:

12
Back to list

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.