hello, 

when i am trying to add an eNodeB to eSight, but the synchornization failed. 

Is it necessary to synchrozine/ upload a certificate? If yes, how to do it? Thanks

Featured Answers

Recommended answer

Neil_Tong
Created Nov 12, 2019 12:02:44

Hi dear,

there are some common causes about your issue:

1. The network between the device and eSight is disconnected.

2. The SNMP configuration on the device is incorrect.

3. The setting of SNMP timeout interval is incorrect.


You can check it as below steps:

1. Check the current network configuration. For example, check whether the device and eSight can ping each other. If the link between eSight and the device is reachable uni-directionally, configure the corresponding route.

2. Check whether the SNMP configuration on the device is correct.

    2.1 Telnet to the device failing to be synchronized.

    2.2 Run the display current-configuration | include snmp command to check the device configuration.

SNMP


3. Check the SNMP timeout interval setting.

    Access the NE Explorer, choose Protocol Parameters > SNMP Parameters in the navigation tree, and check the timeout interval. If the interval is too short, set it to a larger value, for example, 60s.


4. If the fault persists after the preceding operations, contact Huawei engineers.


View more
  • x
  • convention:

All Answers

Hi dear,

there are some common causes about your issue:

1. The network between the device and eSight is disconnected.

2. The SNMP configuration on the device is incorrect.

3. The setting of SNMP timeout interval is incorrect.


You can check it as below steps:

1. Check the current network configuration. For example, check whether the device and eSight can ping each other. If the link between eSight and the device is reachable uni-directionally, configure the corresponding route.

2. Check whether the SNMP configuration on the device is correct.

    2.1 Telnet to the device failing to be synchronized.

    2.2 Run the display current-configuration | include snmp command to check the device configuration.

SNMP


3. Check the SNMP timeout interval setting.

    Access the NE Explorer, choose Protocol Parameters > SNMP Parameters in the navigation tree, and check the timeout interval. If the interval is too short, set it to a larger value, for example, 60s.


4. If the fault persists after the preceding operations, contact Huawei engineers.


View more
  • x
  • convention:

what about the certificate? cause i asked about it
View more
  • x
  • convention:

Of course, you are advised to replace the southbound certificate for connecting base stations and core networks to ensure service security.

Certificate update and certificate restoration will cause a short-lived device disconnection. Perform the operation with caution.

The detailed procedures are as follows:

  1. Choose Resource > eLTE > eLTE System Settings > Certificate Management from the main menu.

  2. Update a certificate file.

    1. Set Device type to eNodeB/coreNetwork based on the site requirements.

    2. Click the icon next to Root certificateServer certificate, and Server private key respectively. In the window that is displayed, select the prepared certificate file and click Open.

    3. Click Update Certificate.

    4. In the displayed dialog box, click Yes.

  3. (Optional) Restore the certificate.

    1. Set Device type to which you want to restore the certificate file.

    2. Click Restore Last or Restore Factory.


View more
  • x
  • convention:

Issue Solved Successfully.
Thank You.
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.