DTSU666-H 250a 50 mA EXPORT LIMITATION

Created: Jul 19, 2021 20:39:13Latest reply: Aug 13, 2021 09:39:58 750 9 0 0 0
  HiCoins as reward: 0 (problem unresolved)

Hello evryone,

i'm an installer, i used a Huawei sun2000-60KTL with a Smart sensor DTSU666-H 250 A 50 mA and a smartlogger3000A, all is normal except  when I activate the injection limitation, the variation of the inverter in relation to the consumption is slow and do not follow consumption perfectly. to identify the problem, i used a network analyzer at the input of the network to compare the value of the smart meter and that of the analyzer and I noticed that the consumption comes from the network even if the solar is sufficient, and the energy comes from the network (for example the consumption is 25KW, The solar gives 15KW and the network 10kw but when I deactivate the limitation export, i found that the solar gives 40KW)


there is a solution or a setting that allows rapid variation

and how to set limitation for DTSU666-H 250a 50 ma, should i use CHINT DTSU666 or DTSU666-

Featured Answers

Recommended answer

BetterMing
Created Jul 20, 2021 01:36:30

Hello, dear.


When you enable limiting output, the inverter output is limited and cannot output enough power to supply the load, so a portion of the power needs to come from the grid. 


You can set your power plant to zero power grid connection so that your plant will produce power in relation to your consumption. The power station will only draw power from the grid when it cannot produce power to supply the load. And the power you produce will not be delivered to the grid.

You can refer to this post for the related equipment parameter setting process.

https://forum.huawei.com/enterprise/en/export-limitation-configuration-on-smartlogger3000a/thread/605842-100027


You can use the DTSU666-H, which is no problem.

Thanks!

View more
  • x
  • convention:

All Answers
Thanks for contacting the Huawei community!

We are checking your question and will provide an answer to you shortly...
View more
  • x
  • convention:

Hello, dear.


When you enable limiting output, the inverter output is limited and cannot output enough power to supply the load, so a portion of the power needs to come from the grid. 


You can set your power plant to zero power grid connection so that your plant will produce power in relation to your consumption. The power station will only draw power from the grid when it cannot produce power to supply the load. And the power you produce will not be delivered to the grid.

You can refer to this post for the related equipment parameter setting process.

https://forum.huawei.com/enterprise/en/export-limitation-configuration-on-smartlogger3000a/thread/605842-100027


You can use the DTSU666-H, which is no problem.

Thanks!

View more
  • x
  • convention:

Hi,

But the production of the inverter does not follow the consumption

consumption and production


View more
  • x
  • convention:

BetterMing
BetterMing Created Jul 31, 2021 08:13:11 (0) (0)
Is your inverter output and input normal? What I mean is that if the input is small, the output can only reach the output stage shown in the graph at maximum. If not, you can contact the PV center. Check for you where the problem is.
Email: eu_inverter_support@huawei.com  
Tang_li
Tang_li Created Aug 5, 2021 01:09:34 (0) (0)
Check whether the power control settings on the SmartLogger are correct,
Check whether the cable connection and CT direction of the meter are correct. The arrow points towards the load and inverter.  
PHASE IMBALANCE CAN CAUSE SUCH A PROBLEM ?
View more
  • x
  • convention:

Tang_li
Tang_li Created Aug 13, 2021 09:23:16 (0) (0)
Check whether the power control settings on the SmartLogger are correct,  
Tang_li
Tang_li Created Aug 13, 2021 09:24:16 (0) (0)
Check the method of total power control.  

Ensure that all cables are correctly connected.

this  SmartLogger3000 Commissioning Video can help you
https://support.huawei.com/enterprise/en/doc/EDOC1100143563?section=o007

View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.