Hello, friend. We suggest you check whether the current sensor is installed in the grid side shutdown position. Also, check the direction of the current sensor. The active power of the meter should be positive when the inverter is not generating power and getting energy from the grid.
Trims63
Reply Clearlove7 Created Mar 23, 2022 16:57:48
(0)
(0)
Thank you, I think I have found the problem, the current sensors had been installed on the Inverter spur and not the main grid input cables. The installer installed the spur to the inverter from the main grid cable before the main CB board and he put the current sensors on these, they were installed with the arrow coming from the inverter. I was getting very low Amps and Watts reading regardless the amount of power being used in the house. Reading are looking far more realistic now.