Current imbalance caused by Y harness

Latest reply: Oct 13, 2021 12:50:32 350 1 2 0 0

Problems:

When the current of a branch of the inverter is observed in a project, the current curve is unbalanced between 11:00 and 14 noon on a sunny day.

Onsite check:

According to the onsite feedback, the SmartLogger WebUI viewed the historical data of the inverter. It was found that PV1 (green) was balanced between 12:00 and 13:00 on November 13. It was preliminarily determined that the branch was connected to the Y wire harness. After onsite confirmation, the Y wire harness of the inverter is connected to the PV1 branch.

145258dotsbbn9n7k5ikk3.png

Y harness to PV1

235301trci7a7iaa0sag0r.png

Historical data

The PV1 current + PV2 current is about 26 A.

Note: The maximum MPPT current of the 175KTL inverter is 26 A.

It can be concluded that the unequilibrium is caused by current overloading the maximum current of MPPT1.

 

Good post
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.