Method used to configure the power supply pool for the OSN 9800

11

The OSN 9800 uses power supply pools to achieve load-based flexible power distribution. The power load at the initial network construction stage usually differs from that at the network expansion stage. Flexible power distribution allows you to flexibly configure the rated input current based on the power loads, which achieves power supply expansion without service interruption.

Other related questions:
Power supply requirements of the OSN 9800 P18
PIU boards are used to supply power to the OSN 9800 P18. Rated current: 25 A (�?8 V) Nominal operating voltage: �?8 V DC or �?0 V DC Operating voltage range: �?8 V DC: �?0 V to �?7.6 V �?0 V DC: �?8 V to �?2 V

Power supply requirements for OSN 9800 U16 subracks
Each U16 subrack requires 4 x 63 A power supplies.

Power supply requirements of the OSN 9800 U64/U32
PIU boards are used to supply power to the OSN 9800 U64/U32. Rated current: The current for the PIU boards can be flexibly configured based on the external power supplies. Nominal operating voltage: �?8 V DC or �?0 V DC Operating voltage range: �?8 V DC: �?0 V to �?7.6 V �?0 V DC: �?8 V to �?2 V

Power supply requirements of the OSN 9800 universal platform subracks
PIU boards are used to supply power to the OSN 9800 universal platform subracks. Rated current: 50 A (�?8 V) Nominal operating voltage: �?8 V DC or �?0 V DC Operating voltage range: �?8 V DC: �?0 V to �?7.6 V �?0 V DC: �?8 V to �?2 V

Power supply inputs required by OSN 9800 U16 subracks
Each U16 subrack requires 4 x 63A power supplies.