Environmental corrosion level requirements of storage products

8

1. The corrosion rate of the copper test wafer is lower than 300 ?b per month in compliance with ANSIc/ISAd-71.04 environmental corrosion G1 level.
2. The corrosion rate of the silver test wafer is lower than 200 ? per month in compliance with ANSIc/ISAd-71.04 environmental corrosion G1 level.
You are advised to ask a professional organization to monitor environmental corrosion levels in the equipment room.

Other related questions:
What are the gaseous corrosivity levels
According to ANSI/ISA-71.04-2013 Environmental Conditions for Process Measurement and Control Systems: Airborne Contaminants, the gaseous corrosivity levels are G1 (mild), G2 (moderate), G3 (harsh), and GX (severe)

Is a license required for the 3DC feature of V3 storage products?
3DC uses the remote replication feature. When 3DC is configured, each device needs to contain the remote replication license.

What's the concentration level of corrosive airborne contaminants in a data center
The concentration level of corrosive airborne contaminants in a data center shall meet the requirements listed in the white paper entitled Gaseous and Particulate Contamination Guidelines for Data Centers published in 2011 by American Society of Heating Refrigerating and Air-conditioning Engineers (ASHRAE) Technical Committee (TC) 9.9. According to the Guidelines, corrosive airborne contaminants in a data center shall meet the following requirements: Copper corrosion rate Less than 300 ?/month per ANSI/ISA-71.04-2013 severity level G1. Silver corrosion rate Less than 200 ?/month.