RH1288 V2 rated input power

1

The rated input voltage for the RH1288 V2 PSUs:
? AC PSU: 100 V AC to 240 V AC
? DC PSU: �?8 V DC to �?0 V DC
Note:
The recommended current specification for the external power circuit breaker connected to the server is 32 A AC or higher.
The AC PSU [Emerson 800W-AC (EPW800W-AC)] and DC PSUs do not support high-voltage DC input.

Other related questions:
Differences among RH1288A V2, RH1288 V2, and RH1288 V3
The differences among the RH1288A V2, RH1288 V2, and RH1288 V3 are listed as follows. The servers' specifications are subject to the official website. ? The RH1288A V2 adopts the Huawei Hi1710 management chip (iBMC), and supports Intel? Xeon? E5-2600 v2 series processors, eight DIMM slots, and two LOM GE electrical ports. ? The RH1288 V2 adopts the management software iMana, and supports Intel? Xeon? E5-2600 and E5-2600 v2 series processors, 24 DIMM slots, and GE or 10GE LOM NIC modules. ? RH1288 V3 adopts the Huawei Hi1710 management chip (iBMC), and supports Intel? Xeon? E5-2600 v3 series processors, 16 DIMM slots, and GE or 10GE LOM NIC modules.

Rated input voltage of the PDU on OceanStor 9000 V100R001C01
The rated input voltage of the PDU on OceanStor 9000 V100R001C01 ranges from 100 V AC to 240 V AC; 50 Hz or 60 Hz.

Rated input current of the PDU on OceanStor 9000 V100R001C01
The rated input current of the PDU on OceanStor 9000 V100R001C01 is 63 A.