Connecting to Fusion Solar Smart PV Management System.

200 0 0 0 0

Problem Description

During commissioning of their PV solar system components consisting of a combination of Sun2000 50KTL and Sun2000 60 KTL inverters, the installer’s engineers were facing issues with configuring their devices specifically in connecting the smart logger to the Fusion Solar Smart PV Management System.

Problem analysis and root causes

Step1: ensuring all communication wiring is properly connected without any faulty or wrong links in the network cable and/or the connection to COM ports. The installer checked all connections and made sure that all cables are properly connected and terminated as per the user manual recommendation.

Step2: ensure that the communication settings are properly set up and are inline with the communication method to be used, in this case (wired connection)

While guiding the installer on how to commission the inverters and setup up the communication parameters it was noticed that the problem was related to settings.

As shown in the image below the Smartlogger 3000 wasn’t communicating with the on-site router and therefore couldn’t connect to the PV Management System.

screenshot1


Solution

The Installer was advised to:

Enable “automatically obtain IP address” in case the smartLogger

·         Set the gateway address to the IP address of the router.

·         Ensure that the IP address of the SmartLogger is in the same network segment as the gateway address.

·         Set the domain name server (DNS) address to the IP address of the router or obtain the DNS address from the network  provider.

After following the above steps there was a successful connection between the smart logger and the router. However, still no successful connection was established with the NMS as shown below:

screenshot2


And this is due to selecting the wrong domain name based on the area of operation.

The Installer was advised to change the domain name from intl.fusionsolar.huwei.com to sg5.fusionsolar.huawei.com based on his region. After performing all changes as instructed the SmartLogger was successfully connected to the NMS and the end user was able to monitor his solar system performance through the Fusion Solar Smart PV Management System as shown below:


screenshot3

 

 



Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.