Connect power meter not listed in drop-down list to SmartLogger 1000A

Created: Dec 14, 2019 19:52:40Latest reply: Sep 29, 2020 06:42:13 831 3 0 0 0
  Rewarded HiCoins: 0 (problem resolved)

Hello,

I am trying to connect a power meter Socomec Countis E34 to my smartlogger 1000A.

By default we found the Countis E43 in the drop-down list of the intelligent power meter, and not the E34.

After a quick look, all the parameters seems the same (Baud rate, parity, stop Bit and registry addresses).

When I choose in the drop-down list Countis E43 and connect the E34, I have no values.

I am trying by choosing Other and configure manually all parameters, but was the same, no values (following the procedure of the manual SmartLogger 1000A, User Manual, Issue 02 (2019-01-15) chapter 6.3.8.2 Setting Modbus-RTU Meter Parameters).

Did you know if it's possible to connect the E34 to the SmartLogger.

What is the best way to do that ?

Thanks,

Olivier

Featured Answers

Recommended answer

BetterMing
Created Dec 16, 2019 01:15:34

Hello, Eoxs
Thanks for your feedback. You connected the smart meter according to the user manual and nothing is displayed.
You can check whether the hardware connection is correct and whether the interface is loose,then according to the user manual, manually enter all the parameters that need to be set. If there is still no value displayed, you need to check for hardware failure
Thanks
View more
  • x
  • convention:

All Answers
Hello, Eoxs
Thanks for your feedback. You connected the smart meter according to the user manual and nothing is displayed.
You can check whether the hardware connection is correct and whether the interface is loose,then according to the user manual, manually enter all the parameters that need to be set. If there is still no value displayed, you need to check for hardware failure
Thanks
View more
  • x
  • convention:

Hello,
Now it works.
Problem come from a bad stop Bit configuration.
I have changed 1 to 2 and it works with the pre-configuartion listed for the Socomec Countis E43.
Not need to define and use Other in the type of Power Meter type.
Pre-configuration is working for type E43 and E34
Thanks,
Olivier
View more
  • x
  • convention:

Posted by Eoxs at 2019-12-17 08:03 Hello,Now it works.Problem come from a bad stop Bit configuration.I have changed 1 to 2 and it works ...
I am glad that your problem can be solved. Thank you for sharing your experience.
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.