Got it

Commissioning Procedure for SmartLogger3000 Through FusionSolar

Latest reply: Nov 16, 2021 08:29:48 220 2 3 0 0

Category           : Industrial

Capacity           : 3.6 MWAC

Inverter             : 100ktl Huawei Inverter

1. Download the Fusion Solar App

Download fusion solar

v  First, open a browser in your phone and search solar.huawei.com/apac, then click the dashed-like icon in the upper right;

v  Next, click Download FusionSolar APP;

v  Click Open;

v  Lastly, click Install


2. Commissioning Start up

Start up

v  Commissioning must be done on the site, can also be done online but it is not recommended.


3. Inverter Commissioning Setup

Setup

v  Click Connect;

v  Scan the QR code of the USB-adapter. If QR scan failed, click the Manual connection (recommended).

v  Then click the WLAN, WLAN default password is “Changeme”. Note: For M3 models, WLAN default password is in the right side of the inverter.

v  Check the Current WLAN, if the SSID is right then click Connect (SmartLogger SSID name starts with “Logger” and then followed by _SNnumber, ex : Logger_10298231561).




Note: If SmartLogger’s SSID can’t be found, press the RST button (SmartLogger bottom part) for 3 seconds

Setup 2

v  Once connected, in the Identity Authentication page, the username should be “Installer” for inverter, and “admin” for smartlogger, then the password is 00000a.

v  After that, you will be directed to the Quick Settings page (during first time access), Change the Grid Code to IEC 61727. Change the voltage level accordingly usually, it is either 380/400/440V,

v  For L1 Inverters, change the Grid Frequency to 60 Hz, then fill the rest of the section accordingly.

v  Then, click next

Frequency

v  Click Confirm.

v  If you want to change the login password, click Yes. If not, then click No.

v  For multiple inverter, you can change the address of each inverters to avoid address conflict. Click Settings

v  If you’re using SmartLogger for your project then exit the Quick Settings page. Click the arrow back (<) at the top left of the page. If you use a dongle or for an L1 inverters, you can add the Power Meter and any other devices.

4. Commisioning SmartLogger FusionSolar App – Adding Power Meter

adding power meter

v  To add a Power Meter,  go to Maintenance > then click Device Management

v  Click the icon in the upper-right corner of the page

add power meter

v  Click Add Devices

v  In the Device Type choose Meter, Port Number is based on where the Power Meter is connected in the SmartLogger's COM ports, Address is the default ID of the Power Meter


5. Power Meter Configuration

Power meter configuration

v  Go to Settings;

v  Then in the Intelligent Power Meter Type, select the corresponding Meter you used.

Note: If the Power Meter you used is not in the lists, you need to manually configure it using the SmartLogger’s WebUi (Enspire), you can follow the procedure below.

v  To check the Power Meter data, go to Maintenance > Device Mgmt. > click Meter > then click Running Info


This article contains more resources

You need to log in to download or view. No account? Register

x

Thanks for sharing
View more
  • x
  • convention:

Good
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.