Clearing SmartLogger Alarm 1106-1 AC SPD

303 0 0 0 0

Problem description:

The SmartLogger frequently generates 1106-1 AC SPD fault alarms.

Fault location analysis:

1. Check that the AC SPD is normal.

171356n2zxcgg8cskx8vwk.png

 

2. Measure the DI8 and GND2 ports using the multimeter to the buzzing level. If the ports do not sound, the AC SPD or cable is faulty.

At this site, intermittent disconnection occurs. Check whether the cable is loose.

171357bdm8fdy85vwp6eeh.png

 

3. Remove the DI8 and GND2 cables, and use the multimeter to measure the buzzing level. If the multimeter does not respond, the cables are faulty.

171358k6tif8c239jvcy5z.png

 

4. Check all cables to the AC SPD.

 

Cause:

The AC surge protector is not connected to all ports. After the fault is rectified, the alarm is cleared.

171359bfiaijja6wnrln1p.png

 

 

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.