Hi dear,

I have set up an eLTE environment. How can I determine whether NEs communicate with each other?

Can anyone help me, thanks

Featured Answers

Best answer

Recommended answer

Neil_Tong
Created Nov 20, 2019 06:26:49

Hi dear, look here:

 Step 1     On the eNodeB side, run the Ping command to check whether the S1-U IP address of the core network can be pinged from the eNodeB.

l   Set Source IP to the S1 interface IP address of the eNodeB.

l   Set Destination IP to the S1-U IP address of the core network.

                              1


 Step 2     On the eNodeB side, run the Ping command to check whether the S1-C IP address of the core network can be pinged from the eNodeB.

l   Set Source IP to the S1 interface IP address of the eNodeB.

l   Set Destination IP to the S1-C IP address of the core network.

                               2

 

Step 3     On the eNodeB side, run the Ping command to check whether the O&M IP address of the NMS can be pinged from the eNodeB.

l   Set Source IP to the eNodeB IP address used for connecting the eNodeB to the NMS.

l   Set Destination IP to the O&M IP address of the NMS.

                              3


 

Step 4     On the WebUI of an industry terminal, run the Ping command to check network connectivity.

1.         Choose System > Diagnosis.

2.         Select Ping for Diagnosis method.

3.         In the Target IP or domain text box, enter the IP address or domain name of the server PC.

4.         Specify Timeout.

5.         Click Ping.

The diagnosis results of the Ping command are displayed in the Result area at the bottom.

                              4


Step 5     On the eSight, run the Ping command to check the network connectivity between the industry terminal and the eSight.

1.         Choose Resource > eLTE > Resource Monitor > Industry Terminal.

The Industry Terminal page is displayed.

2.         Click Ping.

The IP Ping window is displayed.

3.         In the IP Ping window, specify Pack Size(Byte) and Times(1-100).

4.         Click Ping.

The IP Ping results are displayed in the text box.

                              5


View more
  • x
  • convention:

All Answers

Hi dear,

After the core network, eNodeB, and switch configurations are complete, you can run the Ping command to check whether the network communications are normal to rule out bottom-layer link faults.


View more
  • x
  • convention:

Hello,

1.1 GNE Disconnection

Symptom

The icon of a GNE is gray. According to the GNE tab of the DCN Management window, the GNE is being connected.

Possible Causes

The U2000 fails to establish a TCP connection with the GNE or the established TCP connection is interrupted.

Procedure

   Step 1      Check whether the GNE has a reachable socket connection.

1.         Choose Administration > DCN Management from the main menu.

2.         In the DCN Management window, click the GNE tab and check the IP address and port of the GNE.

3.         Ping the IP address of the GNE from the U2000 server.

       If the ping test fails, the GNE may be running improperly or the network may be faulty. Then check the running status of the GNE and the network condition.

       If the ping test succeeds, the GNE may be disconnected due to high packet loss rate. Then go to step 4.

4.         On the U2000 server, run the telnet command to test the TCP connection.

If the test fails, contact the device technical support.

   Step 2      Check the ACL of the GNE.

If the U2000 server IP address is prohibited in the ACL, the GNE will be disconnected.

   Step 3      Check whether excess socket connections have been established.

If the NE management process of the GNE has multiple instances, the number of socket connections may reach the maximum limit. Then no more socket connections can be established, rendering the GNE disconnected.

In that event, save socket connections by shutting down unnecessary U2000s and other tools that connect to NEs.

   Step 4      Check the firewall and antivirus software settings.

Incorrect firewall or antivirus software settings will lead to data truncation. Shut down the firewall and antivirus software if disconnection occurs.

   Step 5      Check the running status of the OS.

If a large number of programs are running at the same time, the OS will have to close communications connections, rendering the GNE disconnected.

In that event, stop unnecessary programs.

1.2 Non-gateway NE Disconnection

Symptom

The icon of a non-gateway NE is gray.

Procedure

   Step 1      Check the number of NEs connected to the related GNE.

If more than 50 NEs are connected to the same GNE, the GNE will not be able to forward data correctly, rendering the non-gateway NEs disconnected.

In that event, replan the network structure and adjust the DCN.

   Step 2      Test the communications status of the NE.

1.         Choose Administration > DCN Management from the main menu.

2.         In the DCN Management window, click the NE tab.

3.         On the NE tab, right-click the disconnected NE and choose Test NE from the shortcut menu.

The U2000 begins to send data to the NE. About 10 seconds later, a failure message is reported. In that event, check that the GNE is properly forwarding data.

1.3 NE Login Failure

Symptom

An NE is properly communicating with the U2000, but its login status shifts between Logged in and Not logged in at an interval of about 5 seconds. The NE_NOT_LOGIN alarm is generated and cleared repeatedly.

Possible Causes

The same NE user is used on another U2000.

Procedure

Shut down a U2000 or switch to another NE user.

Thanks

View more
  • x
  • convention:

Hello,

1.1 GNE Disconnection

Symptom

The icon of a GNE is gray. According to the GNE tab of the DCN Management window, the GNE is being connected.

Possible Causes

The U2000 fails to establish a TCP connection with the GNE or the established TCP connection is interrupted.

Procedure

   Step 1      Check whether the GNE has a reachable socket connection.

1.         Choose Administration > DCN Management from the main menu.

2.         In the DCN Management window, click the GNE tab and check the IP address and port of the GNE.

3.         Ping the IP address of the GNE from the U2000 server.

       If the ping test fails, the GNE may be running improperly or the network may be faulty. Then check the running status of the GNE and the network condition.

       If the ping test succeeds, the GNE may be disconnected due to high packet loss rate. Then go to step 4.

4.         On the U2000 server, run the telnet command to test the TCP connection.

If the test fails, contact the device technical support.

   Step 2      Check the ACL of the GNE.

If the U2000 server IP address is prohibited in the ACL, the GNE will be disconnected.

   Step 3      Check whether excess socket connections have been established.

If the NE management process of the GNE has multiple instances, the number of socket connections may reach the maximum limit. Then no more socket connections can be established, rendering the GNE disconnected.

In that event, save socket connections by shutting down unnecessary U2000s and other tools that connect to NEs.

   Step 4      Check the firewall and antivirus software settings.

Incorrect firewall or antivirus software settings will lead to data truncation. Shut down the firewall and antivirus software if disconnection occurs.

   Step 5      Check the running status of the OS.

If a large number of programs are running at the same time, the OS will have to close communications connections, rendering the GNE disconnected.

In that event, stop unnecessary programs.

1.2 Non-gateway NE Disconnection

Symptom

The icon of a non-gateway NE is gray.

Procedure

   Step 1      Check the number of NEs connected to the related GNE.

If more than 50 NEs are connected to the same GNE, the GNE will not be able to forward data correctly, rendering the non-gateway NEs disconnected.

In that event, replan the network structure and adjust the DCN.

   Step 2      Test the communications status of the NE.

1.         Choose Administration > DCN Management from the main menu.

2.         In the DCN Management window, click the NE tab.

3.         On the NE tab, right-click the disconnected NE and choose Test NE from the shortcut menu.

The U2000 begins to send data to the NE. About 10 seconds later, a failure message is reported. In that event, check that the GNE is properly forwarding data.

1.3 NE Login Failure

Symptom

An NE is properly communicating with the U2000, but its login status shifts between Logged in and Not logged in at an interval of about 5 seconds. The NE_NOT_LOGIN alarm is generated and cleared repeatedly.

Possible Causes

The same NE user is used on another U2000.

Procedure

Shut down a U2000 or switch to another NE user.

hanks

View more
  • x
  • convention:

Hello,
Please refer to the link:
http://support.huawei.com/huaweiconnect/carrier/en/thread-139713-1-1.html
Thanks
View more
  • x
  • convention:

user_3571217
user_3571217 Created Nov 20, 2019 06:19:53 (0) (0)
thanks for your reply  
wissal
wissal Reply user_3571217  Created Nov 20, 2019 06:23:37 (0) (0)
Welcome my friend  
On eNodeB, use DSP S1INTERFACE command to check the status ( optional execute DSP X2INTERFACE, if configured )
On core network side , use PING command to check connectivity on S5, S6 and S11 interfaces.
For trunking network, use PING to test connectivity over Tx and Rx interfaces
View more
  • x
  • convention:

user_3571217
user_3571217 Created Nov 20, 2019 06:21:30 (0) (0)
thanks, is there a more detailed method of operation?  

Hi dear, look here:

 Step 1     On the eNodeB side, run the Ping command to check whether the S1-U IP address of the core network can be pinged from the eNodeB.

l   Set Source IP to the S1 interface IP address of the eNodeB.

l   Set Destination IP to the S1-U IP address of the core network.

                              1


 Step 2     On the eNodeB side, run the Ping command to check whether the S1-C IP address of the core network can be pinged from the eNodeB.

l   Set Source IP to the S1 interface IP address of the eNodeB.

l   Set Destination IP to the S1-C IP address of the core network.

                               2

 

Step 3     On the eNodeB side, run the Ping command to check whether the O&M IP address of the NMS can be pinged from the eNodeB.

l   Set Source IP to the eNodeB IP address used for connecting the eNodeB to the NMS.

l   Set Destination IP to the O&M IP address of the NMS.

                              3


 

Step 4     On the WebUI of an industry terminal, run the Ping command to check network connectivity.

1.         Choose System > Diagnosis.

2.         Select Ping for Diagnosis method.

3.         In the Target IP or domain text box, enter the IP address or domain name of the server PC.

4.         Specify Timeout.

5.         Click Ping.

The diagnosis results of the Ping command are displayed in the Result area at the bottom.

                              4


Step 5     On the eSight, run the Ping command to check the network connectivity between the industry terminal and the eSight.

1.         Choose Resource > eLTE > Resource Monitor > Industry Terminal.

The Industry Terminal page is displayed.

2.         Click Ping.

The IP Ping window is displayed.

3.         In the IP Ping window, specify Pack Size(Byte) and Times(1-100).

4.         Click Ping.

The IP Ping results are displayed in the text box.

                              5


View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.