Can strings PV1 and PV2 connected in series in a SUN2000-5KTL inverter

Created: 2 days 18:30Latest reply: Apr 20, 2022 09:44:35 80 3 0 0 0
  HiCoins as reward: 0 (problem unresolved)

I've upgraded the 11 solar modules connected in one string (PV1) from 330w to 450w and I'm experiencing two issues:


1) AC Output is limited to 4kW


I've reviewed the statiscal information of the old pannels and all the maximum peaks in the last two years are just 4000w, so I wonder is there any power limitation per string.


2) In partially cloudy conditions the inverter is suffering unexpected shutdowns with no alarms and apparently due to voltalge higher than 500v in the connected string.


This only happens with the new solar modules


The new solar modules have the following parameters:

Pmax     450w

Vmp     41V

Imp    10.98A

Voc    49.6V

Isc    11.53A


One possible solution I'm considering is to split in two strings (6+5) connected to PV1 & PV2, but someone suggested to interconnect  PV1 & PV2 putting them in serial, so I would like to know if this can be done??


In addition in FusionSolar String configuration mentions PV strings are connected in 2-in-1 mode or "2-in-1 string", does this refers to the previous mentiones configuration?


Thanks in advance,


Enrique

Featured Answers

Recommended answer

Clearlove7
Admin Created Yesterday 08:29

Hello, friend.

According to your situation, we cannot view your power station online. You are advised to seek help from the PV center to obtain a solution. Send an email to the following email address describing your problem and attaching your device's SN number.

Europe Email: eu_inverter_support@huawei.com    

China and Asia Pacific: solarservice@huawei.com     

Latin America Email: la_inverter_support@huawei.com 

View more
  • x
  • convention:

All Answers
Hello User. we are reviewing your question and we will answer you shortly. Thanks.
View more
  • x
  • convention:

Hello, friend.

According to your situation, we cannot view your power station online. You are advised to seek help from the PV center to obtain a solution. Send an email to the following email address describing your problem and attaching your device's SN number.

Europe Email: eu_inverter_support@huawei.com    

China and Asia Pacific: solarservice@huawei.com     

Latin America Email: la_inverter_support@huawei.com 

View more
  • x
  • convention:

@ePVuser if you are using only one string connected, indeed, the output power of inverter will be limited so it is recommended to use both strings (to balance the input).
Also, if the voltage is higher than 500V and battery is connected to inverter, it will prompt an alarm so please check the installation way, inverter may be damaged.
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.