Battery fails to charge from PV production

Created: Apr 29, 2021 11:17:23Latest reply: May 1, 2021 23:02:05 738 6 0 0 0
  Rewarded HiCoins: 0 (problem resolved)

We have an anomaly to one of Huawei system installed this weekend and need your help.

Basically the issue is the smart meeter measures wrongly the consumption and never sees there is surplus energy from panels, and therefore battery is never charged. Have a look at the attached pictures.

I could clearly see the system was feeding into the grid (house energy meter turning fast backwards, while the application was showing consumption from the grid , also high house consumption, and almost zero battery charge and no feed-in. Which is false as system was feeding in energy.  

We have two inverters 4.6KTL(6kwp) with 10kW Luna battery connected and 3 phase power sensor  , and a 2KTL (3kwp) with no battery. I see no alarms in the system. The system discovered itself all components.
I attached more picture with serial nr of devices and their status.

We have 3 phase connection here without neutral, three sensors connected to those three phases with arrow heading house (consumption direction).

Please help identify what is wrong. I assume it could be something with DTSU666-H-3Ph sensors (wrong connected, although they were double checked). Or maybe something else?

Battery is now 16% and is decreasing every day not being charged at all.

1

2

3

4

5

6



Featured Answers
Tang_li
Admin Created Apr 30, 2021 03:27:23

Yes. In grid-tied mode, a meter is required, and most likely your meter has some wiring problems.
Read the user manual carefully.
LUNA2000-(5-30)-S0 Quick Guide
https://support.huawei.com/enterprise/en/doc/EDOC1100160384?idPath=22892350|21439560|7921563|21102413|23448309
LUNA2000-(5-30)-S0 User Manual
https://support.huawei.com/enterprise/en/doc/EDOC1100167258?idPath=22892350|21439560|7921563|21102413|23448309
SUN2000-(2KTL-6KTL)-L1 User Manual
https://support.huawei.com/enterprise/en/doc/EDOC1100136173?idPath=22892350|21439560|7921563|21102413|22027611
View more
  • x
  • convention:

All Answers
Hello, dear.
It's nice to meet you in the community.
We're working on getting the right answer for you. Please rest assured that we'll be back with an answer shortly.
View more
  • x
  • convention:

Hello, dear.
I can see from your diagram that your house consumes a lot of electricity and you are not producing enough to cover the load of your house. You also need to buy power from the grid. How do you still have the extra energy to charge the batteries?
View more
  • x
  • convention:

Hello, in fact here we have a grid owned energy meter that is turning in reverse when power is produced by the solar panels, this meter is turning backwards. The house is not consuming during the day because nobody is actually home to consume. The consumption is later in the evening but the battery is not charging during the times it should. In principle, the battery should charge as the electricity is produced and not used. At least this is what is happening. Has there ever been a case where a battery is failing to charge due to maybe a faulty energy smartmeter?
View more
  • x
  • convention:

BetterMing
BetterMing Created Apr 29, 2021 13:04:17 (0) (0)
Your meter is wired with the positive and negative poles reversed.  
Yes. In grid-tied mode, a meter is required, and most likely your meter has some wiring problems.
Read the user manual carefully.
LUNA2000-(5-30)-S0 Quick Guide
https://support.huawei.com/enterprise/en/doc/EDOC1100160384?idPath=22892350|21439560|7921563|21102413|23448309
LUNA2000-(5-30)-S0 User Manual
https://support.huawei.com/enterprise/en/doc/EDOC1100167258?idPath=22892350|21439560|7921563|21102413|23448309
SUN2000-(2KTL-6KTL)-L1 User Manual
https://support.huawei.com/enterprise/en/doc/EDOC1100136173?idPath=22892350|21439560|7921563|21102413|22027611
View more
  • x
  • convention:

The issue is resolved. The problem was the electrician connected the inverter to the grid side of smart meter not to the house. Once connected to the house all started to work well.  Thanks for your support. 



View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.