hello every one,

today i'd like to ask how do battery capacity test in detailed,

  1. when start this test, when stop it

  2. during test, what notices we have to take


Featured Answers

Recommended answer

BetterMing
Created Jan 7, 2020 08:33:31

Hello, imdo!
Before a capacity test, ensure that: 

  • The UPS is working in normal mode; float charging or hibernation has lasted for 2 hours after the state of charge (SOC) reaches 100%; and the load ratio fluctuation is less than 10%. 

  • The UPS has generated no battery overtemperature, overvoltage, or overcurrent alarm. No generator is connected to the UPS. 

  • The mains, batteries, charger, and discharger are normal. No overload alarm is generated.

NOTE:

The capacity test automatically stops in any of the following cases: 

  • The battery discharge voltage reaches the end of discharge (EOD) voltage plus 0.01 V. 

  • The load fluctuation exceeds 10%. 

  • An alarm is generated. 

When the battery discharge voltage reaches the EOD voltage plus 0.01 V, the test is complete. The test data is used as capacity test data. Save the capacity test data record with the largest discharge capacity in a month as the capacity test data for the month. A maximum of recent 36 capacity test records can be saved.

View more
  • x
  • convention:

imdo
imdo Created Jan 7, 2020 10:05:05 (0) (0)
thanks for your answer,
for example if I put EOD=1.75 per cell=10,5 per battery=420 (40 batteries per string)
so capacity test will end at 420V, how can I confirm if those batteries are good or no (I mean what I will get on UPS screen or data to confirm my result)  
BetterMing
BetterMing Reply imdo  Created Jan 7, 2020 11:39:18 (0) (0)
You can refer this link: https://support.huawei.com/enterprise/en/doc/EDOC1000023395?idPath=9452479|9475817|9487733|7352434  
All Answers

Hello, imdo!
Before a capacity test, ensure that: 

  • The UPS is working in normal mode; float charging or hibernation has lasted for 2 hours after the state of charge (SOC) reaches 100%; and the load ratio fluctuation is less than 10%. 

  • The UPS has generated no battery overtemperature, overvoltage, or overcurrent alarm. No generator is connected to the UPS. 

  • The mains, batteries, charger, and discharger are normal. No overload alarm is generated.

NOTE:

The capacity test automatically stops in any of the following cases: 

  • The battery discharge voltage reaches the end of discharge (EOD) voltage plus 0.01 V. 

  • The load fluctuation exceeds 10%. 

  • An alarm is generated. 

When the battery discharge voltage reaches the EOD voltage plus 0.01 V, the test is complete. The test data is used as capacity test data. Save the capacity test data record with the largest discharge capacity in a month as the capacity test data for the month. A maximum of recent 36 capacity test records can be saved.

View more
  • x
  • convention:

imdo
imdo Created Jan 7, 2020 10:05:05 (0) (0)
thanks for your answer,
for example if I put EOD=1.75 per cell=10,5 per battery=420 (40 batteries per string)
so capacity test will end at 420V, how can I confirm if those batteries are good or no (I mean what I will get on UPS screen or data to confirm my result)  
BetterMing
BetterMing Reply imdo  Created Jan 7, 2020 11:39:18 (0) (0)
You can refer this link: https://support.huawei.com/enterprise/en/doc/EDOC1000023395?idPath=9452479|9475817|9487733|7352434  

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.