Analysis on Low Energy Yield of the SUN2000-60KTL-M0 inverter

250 0 0 0 0

A. Background: In a residential rooftop project in China , the  output power is low after the original 50 kW is expanded to 60 kW. The inverter of a certain brand is replaced with the Huawei SUN2000-60KTL-M0 inverter.

B. Log analysis: Analyze the inverter inspection logs provided by the customer.

1. The following 11 diagrams are the I-V curves obtained from inspection logs. The 12th diagram is the standard I-V curves of other projects for comparison.

2. According to the open-circuit voltage, PV modules 1–6 are one less than PV modules 7–11.

3. The curve of component 6 is the best, and the curves of components 5 and 8 are the worst. Curve 5 has obvious shadow effect. The Imp currents of all PV strings except PV string 6 decrease greatly.

4. When the temperature is fixed, the Imp current of the PV module changes with the irradiance, but the open-circuit voltage changes slightly. The higher the irradiance, the higher the output power of the module.

For example, when clouds suddenly pass through the sky, the output power of the component decreases because the cloud reduces the irradiance and the Imp decreases. As a result, the output power decreases.

1

2

3

4

5

6

7

8

9

10

11

12

C. Onsite check

1. PV modules are used as the roof onsite. The PV module angle is only 5° and there is a lot of dust on the PV modules.

2. There are poles in the south and block them at noon. It is verified that PV strings 5 and 8 in the log have shadow effects.

3. The SUN2000 outputs 380 V AC power and connects to the grid. A large number of grid overvoltage alarms and grid power failure alarms are generated in the SUN2000 alarm log.

13

14

15

D. Solutions

1. To reduce the inverter protection problem caused by high power grid voltage, perform the following steps to modify the parameters onsite:

Modify the protection parameters: SUN2000app --Special User --Password 00000a -- Set -- Protection Parameters-- Level-1 Overvoltage Protection Threshold --264 V 

2. Clean PV modules periodically to increase the energy yield.


Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.