Analysis of RS485 Communication Disconnection

267 0 2 0 0

Background

In a project, the inverter communicates with the SmartLogger 2000 over RS485, and the inverter near the SmartLogger COM port is disconnected.

Problem Description

The customer in South China reported that the SUN2000-36KTL inverter connected to the SmartLogger 2000 in serial mode over RS485. The SUN2000-1 inverter closest to the COM port of the SmartLogger was disconnected, but the other inverters connected to the SUN2000-36KTL were properly communicating with the SmartLogger. The voltage of the RS485 port on the disconnected inverter is normal. Use a serial port tool to access the disconnected inverter. The response is normal.


Networking Mode


Fault Locating

The onsite sampling RS485 communication is interrupted. The main factors are onsite construction or product quality problems. Therefore, the onsite engineers need to check the problem.

Problem Analysis

The communication link was interrupted due to the product quality. The customer used a multimeter to measure the voltage of the RS485 IN/OUT port. The voltage was 0.5 V. The RS485 cables of other inverters were disconnected and the serial port tool was used to send packets to the faulty inverter. Therefore, the communication failure was suspected to be caused by the RS485 daisy link.


Packets


It is suspected that the RS485 link is abnormal. Therefore, instruct the field engineer to use the serial port tool to access the communication disconnection inverter packet over the COM port of the SmartLogger. The packet returned abnormal garbled characters. Therefore, the inverter is not faulty and the onsite construction needs to be checked.


Packets


The RS485 communications cables are armored shielded cables. The cable sequence is correct and the RS485 port is not pressed. Inquired about the RS485 shielding layer grounding onsite. The customer reported that the shielding layer of each inverter was twisted together and then a ground point was found for grounding, as shown in the following figure.


154448yvnjp0r7blirubtt.jpg


The RS485 shielding layer of each inverter needs to be grounded. Therefore, the onsite construction does not meet the construction requirements. Instruct the site to ground the shielding layer at a single point and restore the communication.

Note

The SUN2000 RS485 shielding layer single-point grounding has been described in the user manual and quick installation guide. The shielding layer of each SUN2000 needs to be grounded only. The SmartLogger or other communications devices do not need to be grounded.

Problem Summary

If the RS485 communication is abnormal, check whether the cable wire sequence is crimped properly, whether the cable is loosely connected, whether the shielding layer is grounded on one side, and whether strong-current signal interference exists.

If the problem is caused by the product, measure the voltage of the RS485 port on the inverter or use a serial port tool to test the inverter packets to check whether the response is normal.

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.