Symptom:

Alarm (ID: 0x1EA620007) indicating that an NIC port is abnormal is reported on DeviceManager and cannot be automatically cleared.


Diagnosis:

  1. In the Management IP Address text box on the hardware management page of DeviceManager, search for the IP address of the node for which the alarm is generated. If the corresponding node is not found, this document is applicable. In this case, rectify the fault by referring to operations described in Solution. If yes, go to 2.

  2. Log in to the faulty node and run the following commands to query its front-end and back-end storage IP addresses:

    cat /opt/fusionstorage/agent/conf/node_cluster_ip

    cat /opt/fusionstorage/agent/conf/node_storage_ip

  3. Run the ip addr | grep -B 2 "Front-end or back-end storage IP address of the faulty node" command to query the name of the corresponding network port. For example, in the following figure, the port name is eth0.

    2_en-us_image_0296761344.png

  4. If the storage IP addresses of the node are not in bond mode, check whether the name of the faulty network port in the alarm information is the same as that of the port name queried in 3. If they are the same, this document is not applicable. Otherwise, rectify the fault by referring to this section.

  5. If the storage IP addresses of the node are in bond mode, run the cat /sys/class/net/Bond port name/bonding/slaves command to check whether the faulty network port is a member port of the bond port. If yes, this document is not applicable. Otherwise, rectify the fault by referring to this section.


Causes:

After a user logs in to DeviceManager and successfully adds a node, the configured storage network port is faulty. As a result, an alarm is generated on DeviceManager. In this case, return to the Configure Storage Network page, remove the faulty node from the cluster, or select another normal network port to configure the storage IP address. After the configuration is successful, the faulty network port is no longer used and monitored. Therefore, the alarm cannot be cleared.


Solution:

Log in to DeviceManager and manually clear the alarm.

Comment

You need to log in to comment to the post Login | Register

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.