An alarm about the PIU board

Created: Mar 31, 2021 07:43:18Latest reply: Mar 31, 2021 08:07:13 309 2 0 0 0
  HiCoins as reward: 0 (problem unresolved)

We have a problem:

Onsite PIU examination didn't find any actual power supply interruption, power cable damage, loose connection in PIU, etc.

NCE

How to solve this problem, please help us, thank you!

Featured Answers

Recommended answer

liqiang185
Admin Created Mar 31, 2021 08:07:13

Dear friend!

0x55 indicates that the first input voltage of the APIU is abnormal.

1. Check whether the first power supply of the device is disconnected. If yes, connect the first power supply. If you really don't plan to do it, please mask the alarm.

2. check whether the first switch of the DC PDU in the cabinet is ON. If not, set the switch to ON

3. After the switch or cable cause is excluded, use a multimeter to check whether the external input power supply voltage is within the normal range. For details, refer to the working voltage range of the power supply board that reports the alarm. If the voltage is beyond the normal range, check whether the power supply of the equipment room is faulty.

4. As to the PIU board, if the external input power supply voltage is normal, but the alarm persists, the DC PDU switch may be faulty. Replace the DC PDU switch.

5. After the above causes are excluded if the alarm persists, replace the faulty power supply board.


For more information, please click the following link:

POWER_FAIL

If you do not have permission to open the above link, please click How do we upgrade our account.

Thanks!



View more
  • x
  • convention:

All Answers
Dear friend!
Please rest assured that we'll be back with an answer shortly.
View more
  • x
  • convention:

Dear friend!

0x55 indicates that the first input voltage of the APIU is abnormal.

1. Check whether the first power supply of the device is disconnected. If yes, connect the first power supply. If you really don't plan to do it, please mask the alarm.

2. check whether the first switch of the DC PDU in the cabinet is ON. If not, set the switch to ON

3. After the switch or cable cause is excluded, use a multimeter to check whether the external input power supply voltage is within the normal range. For details, refer to the working voltage range of the power supply board that reports the alarm. If the voltage is beyond the normal range, check whether the power supply of the equipment room is faulty.

4. As to the PIU board, if the external input power supply voltage is normal, but the alarm persists, the DC PDU switch may be faulty. Replace the DC PDU switch.

5. After the above causes are excluded if the alarm persists, replace the faulty power supply board.


For more information, please click the following link:

POWER_FAIL

If you do not have permission to open the above link, please click How do we upgrade our account.

Thanks!



View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.