Alarms Generated in PV Diesel Hybrid Solution with high loads and Suggested Remedy + Comments on Quality of installation

Latest reply: Jan 12, 2020 20:49:14 677 5 0 0 0

Basic System Synopsis: The project is installed in an Industrial Recycling unit and there is no utility grid. Two big Diesel Generators of 650KVA Size run at day time to run the big crushing machines. At evening 1 x 150KVA runs to miscellaneous load when the crushing machines turns off. Client has installed 189KWp PV System with 3 x 60KTL-M0 inverters in parallel to Diesel Genators. Instead of smartlogger, they are using a third party data logger and monitoring platform. Following Alarms were reviewed and remedies suggested based on the log report of one of the inverters. Plant has been under since 27th June which means it has almost 18 weeks till test day.

 

Alarm ID:  2032  (Major)

Number of times occurred: 5 times, different dates

No.

Alarm serial No.

Severity

Child device ID

Alarm ID

Alarm generation time

Alarm clearance time

Reason ID

1

1

Major

4100

2032

6/25/2019 6:01

6/25/2019 6:01

1

 Findings and Proposed solution

Reason Description

Possible Reason

Remedy

Grid Failure for few seconds and then getting back live.

The diesel generators losses output for few seconds and get back

The alarm disappears automatically after the diesel generators power recovers. No special maintenance required.

 

Alarm ID: 2011  (Major)

Number of times occurred: 1 time only

No.

Alarm serial No.

Severity

Child device ID

Alarm ID

Alarm generation time

Alarm clearance time

Reason ID

2

4

Major

4100

2011

6/27/2019 11:40

6/27/2019 11:44

11

Findings and Proposed solution

Reason Description

Possible Reason

Remedy

String 11 was connected reverse  and cleared within 4 minutes. This problem happened only once."

This could be because of reverse polarity connection.

The problem is solved but   remember in this case to check whether the PV string is reversely connected to the SUN2000. If yes, wait until the solar irradiance decreases to a level   when the PV string current reduces to below 0.5 A. Then turn off the two DC   switches and correct the PV string connection.

 

Alarm ID: 2034  (Major)

Number of times occurred: 7 times, different dates

No.

Alarm serial No.

Severity

Child device ID

Alarm ID

Alarm generation time

Alarm clearance time

Reason ID

5

13

Major

4100

2034

7/22/2019 5:54

7/22/2019 5:54

1

My findings and proposed solution:

Reason Description

Possible Reason

Remedy

High Grid voltage sensed for   longer than HVRT Duration but cleared immediately

Possible reason would be sudden   high load disconnection resulting to surge of voltage.

If you have confirmed that the   grid connection voltage exceeds the upper threshold and obtained the consent   of the Huawei Service team, modify the upper voltage protection threshold via   SUN2000 APP as special user.

 

Alarm ID: 2036  (Major)

Number of times occurred:

Plant operation period: 34 times, different days, frequently in a day.

No.

Alarm serial No.

Severity

Child device ID

Alarm ID

Alarm generation time

Alarm clearance time

Reason ID

6

14

Major

4100

2036

7/22/2019 5:54

7/22/2019 5:54

1

My findings and proposed solution:

Reason Description

Possible Reason

Remedy

Grid over-frequency sensed for   few seconds

Possible reason would be sudden high load disconnection resulting to surge of frequency.

Since alarm occurs frequently   then change frequency limits via special user. modify the power grid   over-frequency protection threshold via SUN2000 APP as special user after   taking permission from Huawei service team.

 

Alarm ID: 2033  (Major)

Number of times occurred: 3 times, different dates

No.

Alarm serial No.

Severity

Child device ID

Alarm ID

Alarm generation time

Alarm clearance time

Reason ID

9

17

Major

4100

2033

8/6/2019 16:18

8/6/2019 16:19

1

My findings and proposed solution:

Reason Description

Possible Reason

Remedy

The grid voltage is below the   lower threshold or the low voltage duration has lasted for more than the value specified by LVRT

This has possibly occurred because a high load is connected to the system suddenly which has reduced the output voltage of diesel generators.

If you have confirmed that the grid connection voltage goes below lower threshold and obtained the consent of the Huawei Service team, modify the lower voltage protection threshold via   SUN2000 APP as special user.

 

Alarm ID: 2037  (Major)

Number of times occurred: 13 times, which includes 12 alarms only on 18th October.

No.

Alarm serial No.

Severity

Child device ID

Alarm ID

Alarm generation time

Alarm clearance time

Reason ID

10

18

Major

4100

2037

8/6/2019 16:18

8/6/2019 16:19

1

My findings and proposed solution:

Reason Description

Possible Reason

Remedy

The actual power grid frequency   is lower than the standard equirement for the local power grid.

This has possibly occurred because a high load is connected to the system suddenly which has reduced the output frequency of diesel generators.

Since alarm occurs frequently   then change over-frequency limits via special user. modify the power grid   lower frequency protection threshold via SUN2000 APP as special user after taking permission from Huawei service team.

 

Alarm ID: 2012  (Minor)

Number of times occurred: 8 times, in 1st week of operation only.

No.

Alarm serial No.

Severity

Child device ID

Alarm ID

Alarm generation time

Alarm clearance time

Reason ID

64

2

Warning

4100

2012

6/27/2019 9:33

6/27/2019 9:40

11

My findings and proposed solution:

Reason Description

Possible Reason

Remedy

Only a few PV modules are   connected in series to the PV string 11 and hence the string voltage is lower   than that of other PV strings.

This could be because of shadow.  Since this is not recorded as a daily problem on a specific time of the day, therefore it can be due to the shadow of a cleaner who would be doing the cleaning of modules during those duration

It is a warning that does not stops generation  but it is good to avoid shadow during sun hours on the solar string and try cleaning in the evening or very early in the morning.

 

Further based comments are made on the quality of installation:

 

1)      Inverter are facing direct sunlight on heat sink at day time. Proper arrangement of shading has to be done to avoid derating of inverter as summer is very hot in UAE. ( Please refer to attachment picture 1)


2)      Proper sealing of glands has to be done using Silicon sealant to avoid nesting of insects and dusts going inside. ( Please refer to attachment picture 2)

 

3)      Glands has to be properly tightened to insure IP65 rating of inverters. While stripping cables, installation guide must be followed for appropriate stripping lengths advised which is one of the reason that glands do not get tight properly. ( Please refer to attachment picture 3)


 


This article contains more resources

You need to log in to download or view. No account? Register

x

How do you regulate the voltage and the frequency of this system?
View more
  • x
  • convention:

Qadir
Qadir Created Jan 12, 2020 05:24:25 (0) (0)
Install batteries with hybrid controller to stabilize voltage and frequency.  
ecolindres
ecolindres Reply Qadir  Created Jan 12, 2020 05:37:21 (0) (0)
Thanks Qadir, Do you have any support material of that type of configuration? I'm interested in using Huawei inverters and diesel generators to supply energy, and I'm looking for the most efficient way to do it, but I didn't find anything. again thank you very much  
Qadir
Qadir Reply ecolindres  Created Jan 12, 2020 11:03:07 (0) (0)
You need to speak with your Hybrid Controller Supplier and they should have documents to explain about how their solution works.  
instead of glands you can use a connector for the type of tubing you are using. For instance the LFMC has special hermetic connectors, similar to  http://www.okailfittings.com/pic/big/39_0.jpg. The same for the emt.

For the single cables, you can find glands with multiple holes and plugs. You can chose one that has holes large enough for your cable, and plug any open holes. Similar to https://3.imimg.com/data3/QY/RQ/MY-4017564/cable-gland-for-multiple-cable-250x250.jpg
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.