Symptom

 After the V3 storage upgraded to v3r6c20, an IP address address conflict alarm reported.

Alarm Information

144530lg85502ptu25f5tt.png?image.png

Possible Causes

By default, the IPv6 address is configured for the storage management network adapter. In versions earlier than v3r6c20, the IPv6 conflict is not checked. In v3r6c20 and later versions, if multiple sets of storage devices are in the same subnet, an IP address conflict alarm is generated when the version is upgraded to v3r6c20.

Fault Diagnosis

Check whether the alarm information is the management port and whether the alarm is IPv6.

Solution

Modify the IPv6 IPaddress.


Check After Recovery

Alarm disappear

Applicable Versions

v3r6c20



Thank you for sharing.
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.