Actual Load On Each Phase

Created: Aug 16, 2021 05:27:52Latest reply: Aug 17, 2021 19:54:01 635 10 1 0 0
  Rewarded HiCoins: 0 (problem resolved)

Hello Fusionsolar Comunity,
We have a system installed of 12KTL M2,I've set Active Power Control Mode to "Zero Export Limitation".Addition to that this is installed in a residence so phases are not usually balanced so inverter import and export power accordingly.
My question here is can we have the reading of load on each phase on fusionsolar,beacuse as far as my observation fusion solatr only shows total load running.
Is there any feature i'm missing or is it not there?
TIA


Solution:
I think I've figured it out, here it goes:
Yes we dont have the actual load reading but we can let math do the magic.
We have two reading from managment system:
1) Output of inverter on each phase
2)Apms on each phase shown by smart power meter.

Lets come with a senario:
Example
Inverter Output:
Phase 1: 5A
Phase 2: 5A
Phase 3: 5A

Meter reading:
Phase 1: -2A(It means 2A is being imported from grid)
Phase 2: 1A(1A is being exported)
Phase 3: 4A (4A is being exported)

Phase 1: 5+2=7A, it means 7A load is running on phase 1
Phase 2: 5-1=4A, it means 4A load is running on phase 2
Phase 3: 5-4=1A, it means 1A load is running on phase 3

Featured Answers

Best answer

Recommended answer

BetterMing
Created Aug 16, 2021 06:04:59

Hello, dear.
Unfortunately, this is not available and you will have to calculate the access load yourself.
View more
  • x
  • convention:

Hamid_Raza_Naveed
Hamid_Raza_Naveed Created Aug 16, 2021 06:09:23 (0) (0)
Thankyou for your response, is there any way fusion solar readings can help me determine the actual load running on each phase?
@eugen sir is there any method you can help me with?  
BetterMing
BetterMing Reply Hamid_Raza_Naveed  Created Aug 16, 2021 06:12:23 (0) (0)
You can view the power of each phase. You can check the user manual.
https://support.huawei.com/enterprise/en/doc/EDOC1100020898/f00615c5/functions  
Navin_kay
Navin_kay Created Aug 16, 2021 14:20:00 (0) (0)
 

I think I've figured it out, here it goes:
Yes we dont have the actual load reading but we can let math do the magic.
We have two reading from managment system:
1) Output of inverter on each phase
2)Apms on each phase shown by smart power meter.

Lets come with a senario:
Example
Inverter Output:
Phase 1: 5A
Phase 2: 5A
Phase 3: 5A

Meter reading:
Phase 1: -2A(It means 2A is being imported from grid)
Phase 2: 1A(1A is being exported)
Phase 3: 4A (4A is being exported)

Phase 1: 5+2=7A, it means 7A load is running on phase 1
Phase 2: 5-1=4A, it means 4A load is running on phase 2
Phase 3: 5-4=1A, it means 1A load is running on phase 3

 @Confucius @little_fish   Please correct me if i made any mistake calculating this.TIA

View more
  • x
  • convention:

Tang_li
Tang_li Created Aug 18, 2021 02:19:59 (2) (0)
I think it is ok  
All Answers
Hello, dear!
It's nice to meet you in the community.
We're working on your problem. Please be patient.
View more
  • x
  • convention:

Hello, dear.
Unfortunately, this is not available and you will have to calculate the access load yourself.
View more
  • x
  • convention:

Hamid_Raza_Naveed
Hamid_Raza_Naveed Created Aug 16, 2021 06:09:23 (0) (0)
Thankyou for your response, is there any way fusion solar readings can help me determine the actual load running on each phase?
@eugen sir is there any method you can help me with?  
BetterMing
BetterMing Reply Hamid_Raza_Naveed  Created Aug 16, 2021 06:12:23 (0) (0)
You can view the power of each phase. You can check the user manual.
https://support.huawei.com/enterprise/en/doc/EDOC1100020898/f00615c5/functions  
Navin_kay
Navin_kay Created Aug 16, 2021 14:20:00 (0) (0)
 

Here are referance images @BetterMing

Inverter

Power Meter

WebUi


View more
  • x
  • convention:

BetterMing
BetterMing Created Aug 16, 2021 07:32:18 (0) (0)
This item is not counted in the Fusionsolar system.  
Good
View more
  • x
  • convention:

I think I've figured it out, here it goes:
Yes we dont have the actual load reading but we can let math do the magic.
We have two reading from managment system:
1) Output of inverter on each phase
2)Apms on each phase shown by smart power meter.

Lets come with a senario:
Example
Inverter Output:
Phase 1: 5A
Phase 2: 5A
Phase 3: 5A

Meter reading:
Phase 1: -2A(It means 2A is being imported from grid)
Phase 2: 1A(1A is being exported)
Phase 3: 4A (4A is being exported)

Phase 1: 5+2=7A, it means 7A load is running on phase 1
Phase 2: 5-1=4A, it means 4A load is running on phase 2
Phase 3: 5-4=1A, it means 1A load is running on phase 3

 @Confucius @little_fish   Please correct me if i made any mistake calculating this.TIA

View more
  • x
  • convention:

Tang_li
Tang_li Created Aug 18, 2021 02:19:59 (2) (0)
I think it is ok  

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.