Hi everyone,

I will share a case about a smart meter connect an RJ485 Serial port of MA5621.


Product Model

MA5621

MA5621V800R312

Problem Description

A smart meter is connected to a serial port of MA5621, and the smart meter was frequently online and offline.

The data center found that a smart meter was frequently online and offline. Online 2 minutes offline 3 minutes then online.


Handling process 

Topology:Smart meter connects with MA5621 by RS485, MA5621 connect OLT, Router, Firewall, F5 to the data center.


1.Checked the configuration of the MA5621, no abnormality was found.

2.Compared with another normal MA5621 configuration in the same scenario, no abnormality was found.

3.Replace the MA5621 port.

Change the smart meter from MA5621 0/2/0 to 0/2/1. After the serial connection is configured. the fault persists.


<serialop-config>

serialop-connection 1 port 0/2/1 working-mode TCP-client local-address 

xxx.xxx.xxx.30 local-port xxx6 peer-address xxx.xxx.xxx.10 peer-port xxx6 frame-type 

none

#

[prevlanif]

<prevlanif>

interface vlanifxxx    //Management vlan of the MA5621

interface vlanifxxxx    //Service vlan of the Smart meter

#

[vlanif]

<vlanifxxx>

interface vlanifxxx

ip address xxx.xxx.xxx.189 255.255.248.0   //Management IP address of the MA5621

#

<vlanifxxxx>

interface vlanifxxxx

ip address xxx.xxx.xxx.30 255.255.248.0    //Service IP address of the Smart meter

#


4.Run display serialop-connection


The TCP connection is intermittently disconnected, which occurs every few minutes.


huawei#display serialop-connection

 { all<K>|connectionid<U><1,4294967294>|statistics<K> }:1  


 Command:

          display serialop-connection 1

  Serialop-connection ID  : 1

  Serial port             : 0/2/1

  Mode                    : TCP-Server

  Local Address           : xxx.xxx.xxx.30

  Local Port              : xxx6

  Peer Address            : xxx.xxx.xxx.10

  Peer Port               : xxx6

  Frame Type              : none

  RTU ID                  : 8888

  Connect State           : initialize



5.Ping the IP address of the data center from the MA5621.


The ping operation is intermittently interrupted, which occurs every few minutes.


It is suspected that the IP address of the smart meter configured on the MA5621 conflicts with the IP addresses configured on other devices, or packet loss occurs on the network.


Advise the customer to replace the IP address of the smart meter. If the fault persists after the replace service IP address, we will continue to check whether packet loss occurs on the network.


Replace the service IP address of the smart meter and ping the IP address of the data center. The test result is normal and no packet loss occurs. The TCP connection status is normal. The problem does not recur after one day of observation. After checking the network, it is found that the IP address (IP address before replacement)of this smart meter is the same as the management IP address of the other MDU.


Root Cause

The service IP address of the smart meter conflicts with the management IP address of another MDU.


Solution Description

Replace the service IP address of the smart meter.



Thanks.

The post is synchronized to: Access Network Product Cases

Thanks
View more
  • x
  • convention:

bek7
bek7 Created Mar 5, 2021 17:44:26 (0) (0)
 
Well done my friend.
View more
  • x
  • convention:

Nice one
View more
  • x
  • convention:

Sara_Obaid
Moderator Created Oct 13, 2021 07:34:38

Useful problem analysis and solution description
View more
  • x
  • convention:

Precious
Moderator Created Oct 13, 2021 07:36:55

Good topic. Thank you for the info!
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.