a093 alarm​

Created: Jun 1, 2021 07:02:48Latest reply: Jun 1, 2021 08:36:52 444 4 0 0 0
  Rewarded HiCoins: 0 (problem resolved)
the procedure to handle the a093 alarm?

Featured Answers
E.DR_91
MVE Author Created Jun 1, 2021 07:04:52

Hi AymanOT

please to find below procedure: 

Description
The relative humidity of the control point is higher than the high humidity alarm threshold when the unit starts and the humidity is valid.

Impact on the system
The humidity inside the equipment room is higher than the upper threshold, which may affect the normal operation of the customer equipment.

Possible causes

• The load is low.

• The T/H sensors are located in inappropriate positions.

• The ambient humidity is high. 

• The high humidity alarm threshold is inappropriate.

• The humidity displayed is different from the actual humidity.

Procedure

1. Consult Huawei technical support.

2. Adjust the positions of the T/H sensors. 

3. Check the ambient humidity.

4. Adjust the high humidity alarm threshold.

5. Calibrate or replace the abnormal T/H sensors.


Thank you.

View more
  • x
  • convention:

All Answers
E.DR_91
E.DR_91 MVE Author Created Jun 1, 2021 07:04:52

Hi AymanOT

please to find below procedure: 

Description
The relative humidity of the control point is higher than the high humidity alarm threshold when the unit starts and the humidity is valid.

Impact on the system
The humidity inside the equipment room is higher than the upper threshold, which may affect the normal operation of the customer equipment.

Possible causes

• The load is low.

• The T/H sensors are located in inappropriate positions.

• The ambient humidity is high. 

• The high humidity alarm threshold is inappropriate.

• The humidity displayed is different from the actual humidity.

Procedure

1. Consult Huawei technical support.

2. Adjust the positions of the T/H sensors. 

3. Check the ambient humidity.

4. Adjust the high humidity alarm threshold.

5. Calibrate or replace the abnormal T/H sensors.


Thank you.

View more
  • x
  • convention:

Hello, dear.
What device are you using from Huawei? Can you tell me the exact model?
View more
  • x
  • convention:

AymanOT
AymanOT Created Jun 1, 2021 08:00:20 (0) (0)
NetCol5000-A035  

Hello friend!

ALM-a093 High humidity
Description


The relative humidity of the control point is higher than the high humidity alarm threshold when the unit starts and the humidity is valid.


Impact on the System
The humidity inside the equipment room is higher than the upper threshold, which may affect the normal operation of customer equipment.
Possible Causes
- The load is low.
- The T/H sensors are located in inappropriate positions.
- The ambient humidity is high.
- The high humidity alarm threshold is inappropriate.
- The humidity displayed is different from the actual humidity.
Procedure
1. Consult Huawei technical support.
2. Adjust the positions of the T/H sensors.
3. Check the ambient humidity.
4. Adjust the high humidity alarm threshold.
5. Calibrate or replace the abnormal T/H sensors.

https://support.huawei.com/hedex/hdx.do?docid=EDOC1000116108&lang=en


Thanks!

View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.