A Case of Equipment Grounding Highlighted

Latest reply: Nov 23, 2020 03:50:01 1246 14 8 0 0

Hello everyone!


This post will introduce you a case of equipment grounding. I hope it will be helpful to everyone.

Issue Description

After the power supply device EFS4890 of the OptiX OSN 1500 is powered on, the equipment is powered on normally. However, the equipment personnel finds that the cabinet is also electrified.


Handling Process

1. Check the power supply environment of the equipment room. It is found that the cabinet is not grounded and the power strip connected to the EPS4890 is not grounded. The power supply environment of the equipment room does not meet the requirements.


 2. Analyze the power supply of the cabinet. Connect a ground cable to the equipment room from the outside. Use a multimeter and connect one end to the cabinet and the other end to the ground cable. The voltage of the cabinet is 99 V, as shown in the following figure.

1

3. Further analyze the reason why the cabinet is electrified. Test the voltage of the power supply circuit breaker to the power strip, the voltages of the live wire to the power cable are 220 V, and those of the neutral wire to the ground cable is 0. Therefore, the power supply is normal and no issue occurs.

 

4. There are other vendors' devices in the cabinet (the subracks of the devices are in contact with the cabinet), as shown in the following figure. When other devices are separately powered on, the cabinet is also electrified. When more devices are powered on, the voltage of the cabinet goes up to 160 V. After all devices are powered off, the cabinet is not electrified.

2

 

5. When the device is powered on, connect the ground cable to the cabinet. The voltage of the cabinet changes to 0. The current between the test cabinet and ground cable is almost 0. The fault is caused by the induced voltage, which causes the cabinet to be electrified.


Root Cause

The devices in the equipment room are not properly grounded.


Solution

Ground the cabinet and devices properly.


Suggestions

The grounding of the equipment room should meet the requirements, as shown in the following table.

3

That's all. If you also encounter this problem, please leave a message and share your process.

Thank you!


It 's very important to check the equipment grounding after installation.
I share the post : https://forum.huawei.com/enterprise/en/equipment-grounding-check/thread/594606-100027
Thanks @liqiang185
View more
  • x
  • convention:

Thank you for sharing.
View more
  • x
  • convention:

Thank you
View more
  • x
  • convention:

Thank you
View more
  • x
  • convention:

hmmm
View more
  • x
  • convention:

Good for sharing
View more
  • x
  • convention:

good
View more
  • x
  • convention:

:)
View more
  • x
  • convention:

Good
View more
  • x
  • convention:

12
Back to list

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.