Hello!


This post enquires about an issue with 3 x SUN2000 L1 5kW Inverters across 3-Phase Supply. Please see below for a detailed description.


ISSUE DESCRIPTION


A customer would like to install 3 x 5kW inverters with 5kW of PV, with each inverter wired to a different phase. His preference is for this solution, as he doesn't want to have a single point of failure with one larger 3-Phase inverter.


A few questions:


  • Can these inverters be set up in a master/slave configuration, even across different phases?


  • Will the monitoring show 3 separate sites or can this all be combined into one?


  • Are there any downsides of this solution compared with a single 3-Phase inverter?


Thank you in advance for shedding some light over this issue with 3 x SUN2000 L1 5kW Inverters across 3-Phase Supply!

Featured Answers

Recommended answer

Tang_li
Admin Created Jan 10, 2022 01:52:44

I don't think there's any problem with this solution, and it'll be advantageous in terms of zero power grid-tied control.

1. In master/slave configuration is only the communication networking mode, which can be set to master/slave,

2. Monitoring If you use an SDongle to cascade the communication of inverters, you can combine them into one site. Of course, you can also use 3 SDongles to divide into three sites.

3. From my point of view, there are no drawbacks. The three inverters can be connected to 15 kW, and more than 5 kW.


View more
  • x
  • convention:

simchamnan
simchamnan Created Jan 10, 2022 05:30:25 (0) (0)
 
All Answers

I don't think there's any problem with this solution, and it'll be advantageous in terms of zero power grid-tied control.

1. In master/slave configuration is only the communication networking mode, which can be set to master/slave,

2. Monitoring If you use an SDongle to cascade the communication of inverters, you can combine them into one site. Of course, you can also use 3 SDongles to divide into three sites.

3. From my point of view, there are no drawbacks. The three inverters can be connected to 15 kW, and more than 5 kW.


View more
  • x
  • convention:

simchamnan
simchamnan Created Jan 10, 2022 05:30:25 (0) (0)
 
Good
View more
  • x
  • convention:

Installed 3 units 5KTL-L1 on 3phases
Running fine no problem.
Setting, Commisioning done on master Inverter will propagate to slaves.
Use smartdongle and 3P powersensor if you need to have zero export.3 x SUN2000 L1 5kW Inverters across 3-Phase Supply-4591829-1
View more
  • x
  • convention:

Tang_li
Tang_li Created Jan 11, 2022 01:18:56 (0) (0)
Nice!  
Tang_li
Tang_li Created Jan 11, 2022 01:50:44 (0) (0)
Three single-phase meters can be considered.  
Ken.e
Ken.e Reply Tang_li  Created Jan 11, 2022 03:14:23 (0) (0)
Yes, you could but you have to pull extra RS485 cables from panels to inverter. and inverter com port will full of cables,

RS485 at master
Batt comm,
Inverter cascading (to Slave),
Luna enabler,
Powersensors,
DI contact  
Tang_li
Tang_li Reply Ken.e  Created Jan 11, 2022 03:18:17 (0) (0)
Yes, but it would be much better in terms of power three-phase balancing  
Diagram
View more

This article contains more resources

You need to log in to download or view. No account? Register

x
  • x
  • convention:

Thanks Tang and Ken that was very helpful. Nice looking installation too!
View more
  • x
  • convention:

gzzz
gzzz Created Jan 20, 2022 08:04:13 (0) (0)
 

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.