There are four categories required for room selection. They are given below: Location - Room Obstructions - The area must be free of obstructions that may interfere with the installation of the cable and infrastructure needed to manage the cabling and equipment.
- Cable Chases - The room must be within 10 of an existing telecommunications closet or major network cabling chase or have an area designated for chase space.
- Ceiling Obstructions - The rooms ceiling or the ceiling around the room cannot be obstructed by air conditioning ducts or electrical conduit unless such space has been determined to be allowable.
- Cable Distance - The furthest telecommunications outlet must be within 285ft of the designated telecommunications room area.
- Electrical Devices/Panels - Electrical devices must not be located within or near the selected telecommunications area unless it is at least 10 way from any cable paths or racks.
- Service Closets - The designated telecommunications area must be near service closets and chases so the cost of extending those services is not excessive.
Size - Acceptable Size - Adequate space must be present in the room for racks, UPS power, air-flow, and hardware installation space.
- Size Determination - The telecommunications space shall be sized according to the number of outlets serviced by the designated location and the type of networking hardware required including UPS.
- Additional Space - Extra space shall be designated for special services such as security and other planned devices.
- Distance Around Equipment - A minimum or three feet is required around telecommunications equipment and racks.
Environment - Lighting - adequate lighting is required around racks and punch down boards.
- Air conditioning - The room should have a controlled air environment which does not allow the room to exhibit temperature extremes.
- Airflow - Constant 24 hour air-flow is required in the room so the temperature values are not exceeded in the equipment.
- Security - The area designated for a telecommunications room must be able to be secured either with a lock or a card reader system.
Electrical Power - Power Circuits- Dedicated power is required for both UPS and non-UPS equipment. Separate circuits shall be installed for both types.
- Power Locations - The UPS power circuit must be within six feet of the designated location of the UPS system within the room.
|