“Single Site Solution Documentation” is used by our operational & maintenance colleagues every day for daily configuration, maintenance, troubleshooting and performance management activities. Link to the library: http://support.huawei.com/carrier/docview?nid=SE0000730849&path=PBI1-7851894/PBI1-7854260/PBI1-7919739/PBI1-19944064 Highlights of the Library: The library has below basic contents: Solution Description: In SingleSite 1.0, Site9102 provides a standard solution when the Mini-shelter and BTS3900(Ver.D) (referred to as BTS3900) share the site. The -48 V DC BTS3900 is embedded in the Mini-shelter, which supplies power to the BTS3900. The Mini-shelter shares the site with the BTS3900 in the following two modes: - "1+1 unit Mini-shelters"+BTS3900
- "1+1+1 unit Mini-shelters"+BTS3900
Figure 1-1 Mini-shelter sharing site with the BTS3900 NOTE: - If the BTS3900 is installed in the Mini-shelter, the Mini-shelter is used as the equipment cabinet. If only the storage batteries are installed in the Mini-shelter, the Mini-shelter is used as the battery cabinet. If the power supply device, customer equipment, and storage batteries (optional) are installed in the Mini-shelter, the Mini-shelter is used as the power cabinet.
- When the Mini-shelter shares the site with the base station, the maximum configuration is 1 BBU+6 RFUs.
1.1 Hardware Model Mini-shelters The Mini-shelter is consisting of cabinet, cooling equipment, power system, and rack. The power cabinet, equipment cabinet, and battery cabinet used in this solution are the 2.1 m high cabinets in ITS1000M V100R003C02. ETP48200-A6 (220 V AC single-phase or 380 V AC three-phase input power) is used for the power supply system. The cooling and rack type of the Mini-shelter are shown in Table 1-1. Table 1-1 Cooling and rack type of the Mini-shelter | Cabinet Type | Cooling Type | Rack Type | | Equipment cabinet | AH3000 | base transceiver station (BTS) rack | | Battery cabinet | PC500D | battery rack | | Power cabinet "1+1 unit Mini-shelters"+BTS3900 | AH1500D&PC500D or AH1500&PC500D | combined rack: standard 19 inch rack+battery rack | | Power cabinet "1+1+1 unit Mini-shelters"+BTS3900 | AH1500 or AH1500D | standard 19 inch rack | NOTE: - AH1500 and AH3000 are intelligent AC heat exchangers, AH1500D is intelligent DC heat exchanger, and PC500D is DC air conditioner. For details about the specifications of those cooling equipment, see "Technical Specifications".
- In 110 V AC dual-live-wire input scenarios, the cooling type of the power cabinet cannot be AH1500.
Base Station BTS3900(Ver.D) (-48 V DC) with a 3 U space for customer equipment is used in this solution. 1.2 Equipment Layout The transmission equipment, digital distribution frame (DDF), GSM antenna and TMA control module (GATM), environment monitoring unit type A (EMUA), environment monitoring unit type B (EMUB), SLPU (monitoring), SLPU (transmission), DCDU-12C and ACDB are installed in the space for customer equipment in the Mini-shelter or BTS3900. Table 1-2 describes the equipment configuration principles. Table 1-2 Equipment configuration principles | Equipment | Optional/Mandatory | Maximum Quantity | Remarks | | Transmission equipment | Optional | - | - The power consumption of a single piece of transmission equipment does not exceed 800 W and the power consumption of all pieces of transmission equipment does not exceed 800 W.
- The heat consumption of a single piece of transmission equipment does not exceed 600 W and the heat consumption of all pieces of transmission equipment does not exceed 600 W.
- Six or fewer links of power supply are required for the transmission equipment.
- Maximum 5 U installation space is required for the transmission equipment.
| | DDF | Optional | 1 | Configure the DDF when the transmission mode of the base station is E1/T1. | | GATM | Optional | 2 | Configure the GATM when the DRFU is used as the RFU. | | EMUA/EMUB | Optional | 1 | Configure the EMUA or EMUB when the dry contact alarms quantity is 17 to 32. | | SLPU (monitoring) | Optional | 1 | Configure the SLPU (monitoring) when the dry contact alarms quantity is 1 to 16. | | SLPU (transmission) | Optional | 1 | Do not configure the SLPU (transmission) when the transmission equipment is installed in the Mini-shelter. Configure the SLPU (transmission) when the transmission equipment is not installed in the Mini-shelter. NOTE: The space for customer equipment in the BTS3900 is reserved for the GATMs, not for the transmission equipment. | | DCDU-12C | Optional | 1 | Configure the DCDU-12C when the BLVD circuit breakers on the ETP48200 in the Mini-shelter are insufficient. | | ACDB | Optional | 1 | Configure the ACDB according to the customer requirement. | Layout principles - The GATM is installed in the space for customer equipment in the BTS3900.
- The SLPU (monitoring), EMUA, or EMUB is installed in the bottom 1 U space for customer equipment in the lower part of the equipment cabinet.
- The SLPU (transmission) is installed in the top 1 U space for customer equipment in the lower part of the equipment cabinet.
- Equipment in the space for customer equipment in the lower part of ETP48200 in the power cabinet is installed from top down in the following sequence: DDF, DCDU-12C, transmission equipment, and ACDB.
- The DDF and transmission equipment are preferentially installed in the space for customer equipment in the lower part of the ETP48200. If the space for customer equipment in the lower part is not enough, install the ACDB and passive equipment in the space for customer equipment in the upper part of the ETP48200.
Layout Examples Figure 1-2 "1+1 unit Mini-shelters"+BTS3900 Figure 1-3 "1+1+1 unit Mini-shelters"+BTS3900 1.3 Power Distribution AC Power Distribution The ETP48200-A6 in the Mini-shelter converts one AC power input into two or three AC power outputs to providing power for the cooling equipment and service outlet unit (SOU). Table 1-3 AC power distribution | Power Device | Power Distribution Type | Circuit Breaker Specifications | Power-Consuming Device | | ETP48200-A6 | AC input | 63 A/3 P x 1 | N/A | | AC output | 16 A/1 P x 1 | AH3000 | | 16 A/1 P x 1 | AH1500 or reserved | | 20 A/1 P x 1 | SOU or reserved | DC Power Distribution The ETP48200-A6 in the Mini-shelter converts the AC power to -48 V DC power to providing power for the base station, transmission equipment, cooling equipment, storage batteries, and lamp. Table 1-4 DC power distribution | Circuit Breaker Type | Circuit Breaker Specifications | Silkscreen | Power-Consuming Device | | LLVD | 80 A x 2 | F1, F2 | DCDU-12A in the BTS3900 (supplying power to RFUs, FAN 03C, BBUs, GATMs, and EMUA or EMUB). | | BLVD | 63 A x 1 | F3 | Transmission equipment, DCDU-12Ca, or reserved | | 32 A x 1 | F4 | AH1500 or AH1500D | | 16 A x 1 | F5 | AH3000 | | 16 A x 1 | F6 | PC500D | | 16 A x 1 | F7 | Transmission equipment, lamp, or reserved | | Battery disconnection | 125 A x 2 | - | Storage batteries | | a: When the BLVD circuit breakers are insufficient, the DCDU-12C (supplying power to transmission equipment) must be configured. | 1.4 Monitoring Principles Alarm signals from the Mini-shelter and BTS3900 are reported to the BBU through an RS485 serial cable. Then, the BBU reports alarms to the U2000, allowing the U2000 to manage the Mini-shelter and BTS3900. Monitoring Board Configuration Customized alarms related to customer equipment are collected by the following boards: - USLP2 in the signal lightning protection unit (SLPU): The SLPU supports a maximum of two USLP2 boards, and each USLP2 supports a maximum of eight dry contact alarm signals.
- EMUA/EMUB: It supports four analog monitoring signals and 32 dry contact alarm signals at most.
Therefore, an EMUA or EMUB is required when customized alarms are reported using analog signals, and related monitoring boards are required when customized alarms are reported using dry contacts. The following table lists the required boards for monitoring dry contact alarm signals. Table 1-5 Monitoring board configuration | Number of Alarm Signals | Monitoring Board | | 1 to 16 | USLP2 in the SLPU | | 17 to 32 | EMUA or EMUB | Monitoring Principles Figure 1-4 shows the monitoring principles when one GATM and one EMUA are configured. NOTE: The following figures take the EMUA as an example. The monitoring port on the EMUB is COM_485. Figure 1-4 Monitoring principles (1) Figure 1-5 shows the monitoring principles when no GATM or EMUA is configured. Figure 1-5 Monitoring principles (2) |