[O&M Master] The OTU_LOF Alarm is Reporting on the OTU at the downstream station.
|
Product OptiX BWS 1600G Fault Type Service Interruption OTU_LOF R_LOS Symptom In a network consisting of the OptiX BWS 1600G systems, the signal flow at stations is as follows: A→B→C→D. A, C and D are OTM stations and B is an OLA station. The LWFS board is configured at stations A and D. The TMRS board is configured at station C. An LWFS board at station A reports the TF alarm and the transmit optical power on the WDM side decreases by 10 dB approximately. The corresponding TMRS board at station C reports the OTU_LOF alarm on the WDM side. The transmit optical power of the TMRS is -60 dBm. The corresponding LWFS at station D reports the R_LOS alarm. Cause ***ysis • The TMRS board at station C is faulty. • The LWFS board at station A is faulty. Procedure Step 1 Replace the TMRS at station C. The problem persists and the transmit optical power of the TMRS remains -60 dBm. Step 2 Replace the LWFS at station A. Then, the problem is solved. |