[O&M Master] High Ambient Temperature causes the SCC board on the OptiX OSN 8800 repeatedly reports COMMUN_FAIL Alarms
|
Product
OptiX OSN 8800
Fault Type
COMMUN_FAIL
Symptom
The SCC board in slot 28 repeatedly reports transient COMMUN_FAIL alarms. Cause ***ysis
Possible causes of the COMMUN_FAIL alarm are as follows:
· Boards on the NE are being reset (cold or warm). · The network cables that cascade subracks do not meet relevant requirements. · Boards are faulty. · Before this fault occurs, the OptiX OSN 8800 at the station runs normally and no operation is performed on it. · On the NMS, check historical alarms and performance events of the OptiX OSN 8800 and the time when they are reported. When the SCC board repeatedly reports transient COMMUN_FAIL alarms, the SCC board reports that the equipment temperature ranges from 70°C to 75°C. Later, An air Con was found to be faulty inside equipment room. · A data ***ysis proves that when the ambient temperature is high, the CPU resources and memory time sequence may be insufficient, and this causes abnormal resets on boards.
Conclusion: When Air Con was repaired and temperature of the equipment room became normal, the COMMUN_FAIL alarm was cleared. |
| it is quite obvious, high ambient temperatures in the equipment room either caused by faulty Air conditioner or high atmospheric temperature, resulting frequent unavoidable alarms for the time being, and may left with some hardware faults, especially in the Raman Amplifiers boards. |