 Issue Description:

On 13/04/2018 around 4:00AM, it’s reported that BTS Clyde experiencing OML Fault alarms and intermittent offline:
f4c112c648ca4271bea79c1cd5e81bef
e5cc0b2463004f648b10a404b1c7ac66
It’s suspected that there was transmission issue which caused the BTS offline.
By checking alarms and logs for whole chain 5, it’s found poor signals between site 089 and 093 which was leading to packets loss. All PTN910s tunnels on this chain were affected by this poor signal issue as shown in below graphs:
abb79049218f4553a198a76f58581c7b

dae33c106b72431ca2aca0e5654d3439
9e6ca93c4731414f8a1110df5e11cc6f
 Handling Process:

1、After changing SFPs of site 089&093&095, bit error alarm (MAC_FCS_EXC) was still there on site 093 Carlingford. Then it was suspected that there was PTN910 hardware issue which was leading to the transmission bit error.

2、Field technician did a loopback by pigtail on site 089-Auburn, the MAC_FCS_EXC alarm couldn’t be cleared by loopback so it’s confirmed that the CXPH card was faulty on site 089 Auburn PTN910.

20c196ca364f4bf885c968369c0b68ee

3、Self-loop test on site 089 Auburn proved this PTN910 had bit error in Tx signal of transmission.The root cause was MAC module of CXPH card in PTN910 got faulty which caused the bit error:

68d58d3590ef45108bf2e10c1f6645f9

4、This was solved by replacing CXPH board on site 089 .

Root Cause:

MAC module of CXPH card in PTN910 was faulty causing port 21 Tx signal having bit errors on Chain 5. 

Solution:

This was solved by replacing CXPH board on site 089 

Suggestions:

1、When “MAC_FCS_EXC” alarms was found, it’s suggested to check fibres and change SFPs of upstream or downstream PTNs.

2、If alarm still exists, reboot upstream or downstream PTNs. 

3、If step 2 can’t clear the alarm, replace upstream or downstream CXPH board.

  • x
  • convention:

Comment Reply

Go to the specified floor
Raluca29     Released on 5 days ago Helpful(0) Helpful(0)

great explanation!
  • x
  • convention:

Comment Reply

wissal     Released on 5 days ago Helpful(0) Helpful(0)

Good work
  • x
  • convention:

Comment Reply

realtm7     Released on Day before yesterday 14:34 Helpful(0) Helpful(0)

Helpful info!
  • x
  • convention:

Comment Reply

Reply
You need to log in to reply to the post Login | Register

If the attachment button is not available, update the Adobe Flash Player to the latest version!
Fast reply Scroll to top