What's Site Selection Requirements

The TR should be

At least 5 kilometers away from heavy pollution sources such as smelteries and coal mines.
At least 3.7 kilometers away from medium pollution sources such as chemical, rubber, and galvanization industries.
At least 2 kilometers away from light pollution sources such as packinghouses and tanyards.
Away from industrial and heating boilers.
Away from dusty roads or sand fields.

If this situation is unavoidable, the doors and windows of the TR should not be facing the pollution sources.

Away from livestock farms.

If this situation is unavoidable, the TR should be in the upwind direction of livestock farms. Note that an old livestock room or fertilizer warehouse should not be used as the TR.

NOTE:
If one or more of these requirements cannot be met, ensure that the TR is situated in the upwind direction of the pollution sources.

The air vents of the TR should be located far away from the exhaust of city waste pipes, large cesspools, and sewage treatment tanks. The TR should be in the positive pressure state. Otherwise corrosive gases will enter the TR and corrode components and circuit boards.

The TR should be at least 3.7 kilometers away from the seaside or salt lakes. If this situation is unavoidable, the TR should be airtight and equipped with air conditioners. In addition, the salt-affected soil cannot be used as construction materials.

It is recommended that the TR be on or above the second floor. If this is impossible, the ground for equipment installation in the TR should be at least 600 millimeters above the highest local flood record.